Why was the RCD not tripping with a N-E short? | Page 2 | on ElectriciansForums

Discuss Why was the RCD not tripping with a N-E short? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,277
Reaction score
5,772
Location
Gloucestershire
I went to a property to carry out an EICR.

Sockets and cooker were RCD protected all the other circuits were not.

I realise there is an order of doing the tests but I thought I would check the RCD test button. It didn't trip. I then did an RCD test and the RCD didn't trip.

Took the cover off the CU, started some dead tests on the ring. N-E 0MΩ.

Upon re-energising the ring the RCD kept tripping instantly as you would expect with a N-E short. However all the sockets had been working fine before I arrived!

After an hour of fault finding (as I couldn't leave him without sockets, even though it was just an EICR) I found a neutral touching a back box as the insulation was broken and there was no grommet. Fixed it and the IR results went to 50MΩ and the RCD then worked as it should. I.e the button tripped it and it tested as 11mS at 5x rated current.

My question is why was the RCD test button not working AND why did it not trip when tested? It only became a working RCD once the fault was found which kind of defeats the object!
 
As with other replies, I’ve had this where I’ve done some work and tested the RCD on its own. Then constantly tripping due to a fault afterwards. I do think if they aren’t tested regularly they get seized and when you do something to send them off, they realise what they’re supposed to do and start working..... especially late on a Friday
 
I've also had it where the customer has kept resetting the RCD until it held. Test button etc had no effect until I isolated and cleared the fault then it would test as normal.
 
Not good enough! You need to find out quick smart and then let me know. I'm too busy making bread and am also about to have a cup of tea! ;)
N-E faults are apiece of cake compared to baking the perfect wholemeal loaf. I think the trick is to knock back the dough mix for long enough; not sure if that fixes RCD issues!
[ElectriciansForums.net] Why was the RCD not tripping with a N-E short?
 
N-E faults are apiece of cake compared to baking the perfect wholemeal loaf. I think the trick is to knock back the dough mix for long enough; not sure if that fixes RCD issues!
View attachment 47845
you going to eat that or use it as a medieval siege weapon?
 

Reply to Why was the RCD not tripping with a N-E short? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
643
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
779

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top