Why was the RCD not tripping with a N-E short? | Page 2 | on ElectriciansForums

Discuss Why was the RCD not tripping with a N-E short? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,292
Reaction score
6,532
Location
Gloucestershire
I went to a property to carry out an EICR.

Sockets and cooker were RCD protected all the other circuits were not.

I realise there is an order of doing the tests but I thought I would check the RCD test button. It didn't trip. I then did an RCD test and the RCD didn't trip.

Took the cover off the CU, started some dead tests on the ring. N-E 0MΩ.

Upon re-energising the ring the RCD kept tripping instantly as you would expect with a N-E short. However all the sockets had been working fine before I arrived!

After an hour of fault finding (as I couldn't leave him without sockets, even though it was just an EICR) I found a neutral touching a back box as the insulation was broken and there was no grommet. Fixed it and the IR results went to 50MΩ and the RCD then worked as it should. I.e the button tripped it and it tested as 11mS at 5x rated current.

My question is why was the RCD test button not working AND why did it not trip when tested? It only became a working RCD once the fault was found which kind of defeats the object!
 
As with other replies, I’ve had this where I’ve done some work and tested the RCD on its own. Then constantly tripping due to a fault afterwards. I do think if they aren’t tested regularly they get seized and when you do something to send them off, they realise what they’re supposed to do and start working..... especially late on a Friday
 
I've also had it where the customer has kept resetting the RCD until it held. Test button etc had no effect until I isolated and cleared the fault then it would test as normal.
 
Not good enough! You need to find out quick smart and then let me know. I'm too busy making bread and am also about to have a cup of tea! ;)
N-E faults are apiece of cake compared to baking the perfect wholemeal loaf. I think the trick is to knock back the dough mix for long enough; not sure if that fixes RCD issues!
[ElectriciansForums.net] Why was the RCD not tripping with a N-E short?
 
N-E faults are apiece of cake compared to baking the perfect wholemeal loaf. I think the trick is to knock back the dough mix for long enough; not sure if that fixes RCD issues!
View attachment 47845
you going to eat that or use it as a medieval siege weapon?
 

Reply to Why was the RCD not tripping with a N-E short? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
691
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top