Also one of the valves has the switch stuck on manual (it has been jammed for some reason) would that cause this issue. I forgot to mentiin this earlier! Sorry.
Discuss Air source heat pump heating issue in the Central Heating Systems area at ElectriciansForums.net
I don't think that's the problem as when the heating is off but hot water on then there is no heat, so the valve seems to be working okCould be your programmer not sending a signal to the valves
As in hot water or heating? If it's the heating valve then id imagine that's the problem and it will just be a case of moving it to auto (if I can free it) or getting a new valve motorCheck which valve is stuck
Before I check the orange wire with a multi meter, I'm looking for 250v on this wire when the heating is on and 0v when heating off right?
Ok so how would I test it to see if it is faulty? Measure resistance?With a multimeter you may get a reading of 240V regardless of whether it is actually live or not.
I would test the connection between the grey and orange wire maybe? What do you recommendIt might have volt free switching. What will you do then?
I will take some tonight about 7pm when I am homeI could, but it would be very expensive as I would charge traveling time + time on site
Photos.
Ok so how would I test it to see if it is faulty? Measure resistance?
Right, before you start pulling things to bits you need to check whether there is power at terminal 9 of the heat pump wiring centre, see page 9 of the manual.
If you have 230 at terminal 9 then the HP is asking the MV to open, if there is no power then the HP is not asking for heating regardless of what the controller says.
I still think this is a parameter error or sensor fault.
If you have power at terminal 9 and no power at the MV then a broken wire you have, or a hidden JB.
The ones I've seen tend to power the MVs from the HP, the orange/grey being used to power pumps via contactors.
Is there and internal wiring centre? If so a loose connection in there may be the cause.
Junction box,Excuse my ignorance but what does JB stand for
It's a Honeywell but it doesn't appear to be working (heating is on no matter temp on stat) EDIT, scrap that, it works fine:It's difficult to see whats going on in that photo otherthan there is a call for heat as the pump is/should be running. I've never seen a buffer used like that before. What room stat do you have?
Junction box,
The one on the wall next to the switches.
You'll probably find a multi core flex going from there to the HP.
One core will go to terminal 9 on the HP and the heating MV should be connected here also.
I'm not sure what the three port is doing, especially in the position it is. Might be a return diverted.
Any joy with the engineers manual?