Job is to replace this extractor fan as in attached photograph, would you say its in zone 1 or 2, i.e. could I replace with mains or would selv be needed not sure if I can get above ceiling to fit transformer.
[ElectriciansForums.net] Shower Zone and fan
 
I have fitted these mains fans which are suitable for zone 1 but I think it is only the standard non timer one which is suitable.
 
In the case of this particular unit with the positioning and height in relation to the shower I'd be looking at a 12 volt fan, although if that's a flat roof or very low pitch fitting the transformer unit could be a bit challenging.
 

Reply to Shower Zone and fan in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Thanks for your thoughts on it. It seems weirdly vague to have some rules like the ipx4 with the addendum of on the proviso it's backed up by a...
Replies
2
Views
779
Met landlord on site as he lives not far away and showed him which filters he needed so he could see for himself. Cooker is on inside wall of a...
2
Replies
17
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top