Commercial/Industrial installation. Summary of installation:

Main feeder pillar contains TNCS incoming supply single phase 100A main fuse, 25mm DNO tails, meter, 100A double pole isolator switch, 25mm tails/16mm CPC to 63A rotary isolator, 10mm SWA cable 25m run to digital advertising panel into a 100A double pole main switch.

Digital advertising panel DB contains 7x C10 RCBOs for the 7 sections of the screen wired in 1.5mm flex.

My question is as follows.. is the main fuse head satisfactory protection for that 10mm SWA cable? Or does it require a switched fuse isolator as it is over 3m in length? Furthermore should it have its own DB and the SWA on a 50A MCB due to the cable size being 10mm and in ducting underground which can only take a maximum of 58 amps.

As it stands that cable has a 63amp rotary isolator & a 100A DP switch before the isolator. Meaning the only protection it has is that 100A main fuse which assuming it actually has a 100A fuse inside doesn’t provide satisfactory overload protection for this cable size in the first place.
 

Reply to Is the main fuse head satisfactory protection for SWA supply cable? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
600
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
636

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top