Socket not working anymore. | Page 4 | on ElectriciansForums

Discuss Socket not working anymore. in the UK Electrical Forum area at ElectriciansForums.net

RDB85

-
Trainee
Joined
Nov 23, 2017
Messages
1,084
Reaction score
168
Location
Liverpool
So last night I noticed that the Socket behind the TV was not working. Plugged in my Kewtech plug tester and nothing. So turned off the MCB for the downstairs sockets. Undone the Socket and its been spurred using new colours from the 13A FCU. Changed the 13A fuse in the FCU, checked the cables and nothing seems out of the ordinary.

There is a socket below that which is wired in Old Colours, which has been there forever. I am just wondering if there is an issue with the FCU, or the wiring itself.

Screwed it all back and then turned the MCB back on. Our house is currently wired in Old Colours, with a Square D CCU. Anyway plugged my socket tester in and again nothing. Would anyone have any ideas what it could be?

Is there any test equipment I could buy to allow me to do some testing, other than a Test Metre as i don't have a lot of money at the moment.
 
OP you could try looking at the YouTube videos on Testing etc, the guy I sent you a video of is very good, there are many equally good presenters in there, worth a look if you are really interested, give it a bash.

Thanks Pete. I’ve seen a few of Chris’s videos before. They are really good. I will have a look at them.
 
So I spoke to my tutor yesterday and luckily they went through safe isolation and then how to test a 3 phase distribution board. I have seen this kit on ebay: Socket And See SP200 proving unit And Socket & See Voltage Tester VIP Pro | eBay - https://www.ebay.co.uk/itm/Socket-And-See-SP200-proving-unit-And-Socket-See-Voltage-Tester-VIP-Pro/293104145650?hash=item443e5e54f2:g:JIEAAOSwKotc69r5

Would that be okay as it seems to be a good price, but I have never heard of the brand. Or shall I just look at a Megger?

Megger:

 
As an eBay Associate we earn from qualifying purchases.
So I spoke to my tutor yesterday and luckily they went through safe isolation and then how to test a 3 phase distribution board. I have seen this kit on ebay: Socket And See SP200 proving unit And Socket & See Voltage Tester VIP Pro | eBay - https://www.ebay.co.uk/itm/Socket-And-See-SP200-proving-unit-And-Socket-See-Voltage-Tester-VIP-Pro/293104145650?hash=item443e5e54f2:g:JIEAAOSwKotc69r5

Would that be okay as it seems to be a good price, but I have never heard of the brand. Or shall I just look at a Megger?

Megger:

Aa long as the kit complies, but Kewtec for me.
 
As an eBay Associate we earn from qualifying purchases.
Just bought an MK FCU. I’ve now safe isolated the circuit. I’ve split it so I have the circuit for the outside light. Which is to the right and then a circuit coming from the top. Old colours are from the socket below and the new colours are from the spurred socket.

Looking at the back of the MK socket it had the supply and load. I am looking at how it was wired previously

Load would be the outside light and the Supply would be the sockets.

Would that be correct?
 
So the old coloured cables are part of the existing RFC and the new colour is a spur socket from the RFC?
 
So the old coloured cables are part of the existing RFC and the new colour is a spur socket from the RFC?

New colours are from the addition socket that is spurred from the FCU. Old colours are from the RFC. As all the sockets downstairs are on a RFC. Which is then has a feed from that socket to the FCU.
 
Socket on the bottom is on a RFC. Which is in old colours. It then has a spur to the FCU above in old colours. There is then flex for the light in old colours in the FCU. Then the final socket is then spurred from the FCU in new colours.

Good news is the outside light works.
 

Attachments

  • [ElectriciansForums.net] Socket not working anymore.
    4A5CDFB2-E203-4E04-B934-393C1E5A3008.jpeg
    1.5 MB · Views: 35
So tried again, bought a new lamp for the outside light. Wired the spur so that the Load Side is the Light and the Supply is the sockets. Tested the socket under the bracket. Still not working with the Socket Tester. Tried the FCU with the new lamp. Nothing.

I then looked at the wiring on the RFC, it seems that one of the live (red) is quite short. It reaches into the socket but barely, so I have got a crimping tool, some blue crimps and some 2.5mm2 T&E. So I am going to try and extend any short cables. Although the socket tester has come back all green lights, showing no faults.
 
So tried again, bought a new lamp for the outside light. Wired the spur so that the Load Side is the Light and the Supply is the sockets. Tested the socket under the bracket. Still not working with the Socket Tester. Tried the FCU with the new lamp. Nothing.

I then looked at the wiring on the RFC, it seems that one of the live (red) is quite short. It reaches into the socket but barely, so I have got a crimping tool, some blue crimps and some 2.5mm2 T&E. So I am going to try and extend any short cables. Although the socket tester has come back all green lights, showing no faults.

So if the light, wired to the new FCU is not working then the problem is going to be before this.
Is your bottom socket functioning ok?
 
Yes the bottom socket is okay. Tested with a socket tester and it’s all green. TV is plugged in and working.

Edit... Brain fart moment...

So just to recap. The bottom socket is working. This wires to the new FCU which is not working.
Are the wires going from the bottom socket to the FCU ok?
 
Edit... Brain fart moment...

So just to recap. The bottom socket is working. This wires to the new FCU which is not working.
Are the wires going from the bottom socket to the FCU ok?

Yes that’s correct. The wiring appears to be okay. No signs of damage. But as mentioned one of the lives although reaches just, is a little short. So I was thinking of maybe adding some blue butt crimps to that and then using some 2.5mm2 twin and earth to extend the cable. Just to see could that be the issue .
 
Yes that’s correct. The wiring appears to be okay. No signs of damage. But as mentioned one of the lives although reaches just, is a little short. So I was thinking of maybe adding some blue butt crimps to that and then using some 2.5mm2 twin and earth to extend the cable. Just to see could that be the issue .

The cable length looked ok in the pics you posted up before, but you are there so you will know... :)
If the light to the new FCU isn't working or the socket wired to the FCU, then it seems to suggest its the cable from the bottom socket to the FCU that may be at fault.
 
The cable length looked ok in the pics you posted up before, but you are there so you will know... :)
If the light to the new FCU isn't working or the socket wired to the FCU, then it seems to suggest its the cable from the bottom socket to the FCU that may be at fault.

Those cables look okay as I say. Would it be okay to do a butt crimp on the live and use the brown from the 2.5 t&e as a new live?
 
Those cables look okay as I say. Would it be okay to do a butt crimp on the live and use the brown from the 2.5 t&e as a new live?

If you need to extend one on the cables then using a butt crimp and descent heatshrink would be one way of doing it.
Someone did post a nice little inline connector (Not Wago) in a past post, that looked good.
 

Reply to Socket not working anymore. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Assuming you are a novice to electrics? As in no access to electrical equipment. Plug something in to the sockets that you know works else where...
Replies
1
Views
303
Cbelectrics
C
  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
607
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
389
  • Question
Recommend this: Electricians Guide to Inspection and Testing Book -...
Replies
18
Views
2K
  • Question
I suspect you have damaged a wire but now it is free from whatever it was shorting on.
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks