Modern wiring help rcd trip | on ElectriciansForums

Discuss Modern wiring help rcd trip in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 24, 2019
Messages
28
Reaction score
5
Location
Derby
Hi all. Newbie please be gentle...

My daughter in law moved into a new [2007] build. All socket circuits 20A radial MCB. One socket circuit trips rcd intermittently when the Wi-Fi router psu plugged in. Psu is double insulated and pat tests ok. Radial tests out ok with 50M ohm at 500v. Nothing obvious in the socket backs. Any ideas what to look at next? I'm here for the day visiting. Thanks!
 

Attachments

  • [ElectriciansForums.net] Modern wiring help rcd trip
    20190817_091949.jpg
    1.1 MB · Views: 118
  • [ElectriciansForums.net] Modern wiring help rcd trip
    20190817_092335.jpg
    3 MB · Views: 374
you could try moving the suspect circuit over to the other side and fit a RCBO.
assuming the 45A is shower, this could do with moving to the RCD side. winner both ways.
 
45A is cooker. It's a rental property that they have just moved into and I'm here on holiday so a bit loath to start rewiring it! Was just after things to look for fault finding. Does 24ma seem low for the trip current?
 
Just curious. It looks like a pre-made connector, designed to slip into the cavity wall behind the back-box, but it must be at the end of the circuit, so not much use anywhere else unless you can connect the next socket somehow, Either way, it looks like you need two sets of connections for the socket...rather than just connecting the cable direct to the socket outlet?
 
Yeah weird wiring. All circuits are radial 20A. No RM here. But each socket has one wire going in only. So there must be a JB in the cavity somewhere.

Anyway whacked a new RCD in, see what occurs.... thanks for all the replies.
 
As above, if this is a rental property then under no circumstances should you be interfering with the electrical installation without the landlord's consent.

The landlord/landlady should be contacted to organise his/her own Electrician.
 
If each socket has just one cable, per the photo, and each one has these "connectors" then clearly there must be a JB, or perhaps several, somewhere. So instead of a supply cable looping in and out we have a JB supplying several sockets, each of which has one of these connectors? So we have 3 terminations per socket? Thus we have extra points of connection that can go wrong? Each socket will be traced back to the JB for fault finding? I do see the logic in this system, and can see an advantage or two, but in reality it seems like a bit of a faff. If those plug-in chaps can't take another cable, you would have to extend the circuit by using the terminals on the socket outlet itself, per usual...and if you feed say 10 sockets from a JB or some other connection outlet, you have a kind of spiders web effect, rather than a true radial?
Just asking...keen to learn.
 
On a different subject I have to say the insulation on the phase conductors where they terminate into the OCPD s are damaged lol, a steptoe and son job
 

Reply to Modern wiring help rcd trip in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K
Perfect!! Thanks a lot gents. You've been massive help this last day 😁
2 3
Replies
43
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top