Pump Control | on ElectriciansForums
Discuss Pump Control in the Talk Electrician area at ElectriciansForums.net
New Zealand
Hi guys, I have a starter rated 440v, and wanted to use it to a pump rated at 220-240 delta/ 380-415 star, is it possible to connect it in delta? or it should only be star?
What's your supply voltage is more importaint.
An what do you mean rated at 440V? As in that's the maximum voltage the starter will take?
What kind of starter is it?
For the OP, you also asked about how you should start the Motor, you need to take in lots of variables, mechanical loading for example, starting currents etc many things need to be considered.
Dependent on how big the pump is, and how much head pressure it has to overcome is another factor.
May also need soft starting/stopping to avoid "water hammer" in the pump/ pipework valves etc..
You will have to run in star. However the voltage is still a bit high.
Would be better with a VSD that you could trim the output to what you require.
Manual for soft start is here:
I should add, you're starter isn't rated at 440v it's 380 - 415 V.
What is your supply voltage?
Yup, you're right, sorry 'bout that, supply voltage's 400V, star indeed.. Thanks mate! Just wanted to confirm before doing it.
Reply to Pump Control in the Talk Electrician area at ElectriciansForums.net
Hi there , I wired it up following the instructions from similar model. Works great thanks for your help
Some year back there was a case of a young girl killed by being sucked down to the bottom of a pool when being emptied through the power drain...