To spur off a RFC with multiple outlets, you must have a Fused spur as the first outlet then your socket outlets as described in the diagram posted earlier, the fuse in question will be a cartridge fuse housed in the fused spur unit max size 13 Amps, hence the max allowed in the socket outlets you feed from that Fused spur unit will be limited to 13 Amps, the RFC may still be protected via a MCB at the CU, does the existing RFC have RCD protection? Hope that makes sense.Help an Aussie understand.
The fuse connected to the spur, where is that physically situated in the installation? alongside the outlet, back in the switchboard, or somewhere else?
and do you guys still use fuses, or is that your name for a breaker?
A ring circuit has two actives in the bottom of the main breaker and two neutrals in the neutral link?
It makes sense (not that I think it is a great way of wiring a circuit). I know the logistics of it, I was more wanting the know the physical location of the fuse. So it is embedded in the socket?Hope that makes sense.
No Mate not imbedded in the socket The switched fused spur unit is a separate unit, roughly the same size as a socket, used for fusing down when you are connecting lower load, difficult to explain to a non Brit, the fi/use is of the type used in 13Amp UK plug tops, google "switched fused unit" it may explain "a picture is worth a thousand words" as they sayIt makes sense (not that I think it is a great way of wiring a circuit). I know the logistics of it, I was more wanting the know the physical location of the fuse. So it is embedded in the socket?
Why are you still using fuses?
It makes sense (not that I think it is a great way of wiring a circuit). I know the logistics of it, I was more wanting the know the physical location of the fuse. So it is embedded in the socket?
Why are you still using fuses?
Were the sockets singles or doubles? Whilst not technically correct it would be acceptable in practice if both sockets were singles, as this would be no different to a double socket on a spur.Hi,
Just need to check something. Sparky installed two new plug sockets. To do this, cut into the main ring, put a junction box in, one cable out to socket. Then from there connected one more plug. I understand to spur off a spur you should use a fuse between them?
A spur is a double socket or a single, so taking two singles us wrong in my bookWere the sockets singles or doubles? Whilst not technically correct it would be acceptable in practice if both sockets were singles, as this would be no different to a double socket on a spur.
No it isn't technically correct at all. I understand your theory but nevertheless it is incorrect advice.Were the sockets singles or doubles? Whilst not technically correct it would be acceptable in practice if both sockets were singles, as this would be no different to a double socket on a spur.
I said it is not technically correct. But if I was doing an EICR two doubles on a spur would be a code 2, two singles would be a code 3. If two singles were butted together they would look like a double, a couple of meters of cable between and suddenly it's a different ball game. Not saying it's compliant but in practice there is no difference whatsoever, the regulations are not statutory and deviation can be justified where equivalent safety is achieved.No it isn't technically correct at all. I understand your theory but nevertheless it is incorrect advice.
Why are you still using fuses?
'Based on this a two gang socket will draw no more than 20a'!!….. Does it have a current limiter then?? A twin socket can, and will, have two 3kw 13a appliances plugged into it just the same as two singles because the plug fits both. The type testing is based on average loadings likely to be applied in average circumstances, the same average circumstances apply whether it is a twin or two singles. British Standards can say what they want, Joe Public will never ever be heard to say. " Ah, two 3kw appliances I need to use, I cant plug those into a twin because it'll only take 20a, I'd better find two separate singles to plug them into".You said not technically correct but acceptable. A two gang socket is type tested with a load of 20A (14A and 6A) across the outlets and whilst in practice this may not be the case it is fact. Based on this a two gang socket will draw no more than 20A, argue this with British Standards. Two one gang sockets have the potential to draw 26A. To apply a departure you could not guarantee a lesser standard of safety is provided by using two one gang sockets.
I believe MK claim their twin sockets are good for 2x13A loadsAs I said in practice this may not be the case.
Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?used for fusing down when you are connecting lower load
Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
I guess it's because the UK wiring systems are the envy of the World!!Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
I replaced quite a few burnt out MK logic sockets that have been used with 2 x 10A+ loadsI believe MK claim their twin sockets are good for 2x13A loads![]()
"Why?" only applies when the spur is to feed more than one point. A fused spur enables a single cable (2.5mm) rated at < the 32a source OCPD to feed any number of points because the load is limited to 13a. Two twin sockets on an unfused spur would have a load potential exceeding the current carrying capacity of a single 2.5mm cable which could result in thermal damage to that cable.Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
Help an Aussie understand.
The fuse connected to the spur, where is that physically situated in the installation? alongside the outlet, back in the switchboard, or somewhere else?
and do you guys still use fuses, or is that your name for a breaker?
A ring circuit has two actives in the bottom of the main breaker and two neutrals in the neutral link?
Take a look at the diagram in post 4 all will become clearHelp an Aussie understand.
The fuse connected to the spur, where is that physically situated in the installation? alongside the outlet, back in the switchboard, or somewhere else?
and do you guys still use fuses, or is that your name for a breaker?
A ring circuit has two actives in the bottom of the main breaker and two neutrals in the neutral link?
The diagram clearly says "one single or one double". it doesn't say two singles equal one doubleBut if I was doing an EICR two doubles on a spur would be a code 2, two singles would be a code 3
This doesn't make any sense at all. Two unfused sockets doesn't equal "unprotected", it is still protected by the 32 amp breaker (just like all the other sockets on the ring circuit). All you are doing is limiting that socket and any connected after it, to 13 amps. it is still part of the 32 amp circuit.Two twin sockets on an unfused spur would have a load potential exceeding the current carrying capacity of a single 2.5mm cable which could result in thermal damage to that cable.
so we stick a fuse in the plug to protect the appliance, saves on copper.
because we cheap and want to save money on copper and circuit breakers.and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? y
I probably didn't say it right, might be my accent.... why are you guys still using fuses? they are old news
It doesn't, and I never said Bs7671 says two singles equals one double. I said in my opinion there is no difference in practice because both allow the connection of any two 13a appliances with a 13a plug.The diagram clearly says "one single or one double". it doesn't say two singles equal one double
You are completely missing the point. A ring is protected by a 32a breaker because each socket on the ring is effectively fed by TWO 2.5mm cables, not one. If you reduce the supply cable to ONE 2.5mm with a spur off the ring then the load carrying capacity of that part of the circuit is effectively halved, it's no longer capable of carrying 32a. That's why the spur cable would need to have a reduced overcurrent device to protect only the spur if it supplies more than one twin outlet.(or more than one single to be in compliance with the guidance in 7671.This doesn't make any sense at all. Two unfused sockets doesn't equal "unprotected", it is still protected by the 32 amp breaker (just like all the other sockets on the ring circuit). All you are doing is limiting that socket and any connected after it, to 13 amps. it is still part of the 32 amp circuit.
If two fused sockets is going to exceed the load potential of 2.5 mm, then what do you think all those other sockets going to do to the current carrying capacity of the 2.5 mm in that circuit?
It clearly does say one single or one double. Look in the top/left square, my friend.It doesn't,
The trouble is, anyone can change that single to a double at a later stage... you now have two doubles.I said in my opinion there is no difference in practice because both allow the connection of any two 13a appliances with a 13a plug.
If you reduce the supply cable to ONE 2.5mm with a spur off the ring then the load carrying capacity of that part of the circuit is effectively halved
You say that like it is a bad thing. Even thou I believe only one would trip.both may trip under fault or overload conditions.
I hope this answers the points you have made, my answers in boldIt clearly does say one single or one double. Look in the top/left square, my friend.
You've misunderstood but I perhaps wasn't clear, when I said ' It doesn't', I was agreeing....it doesn't.
The trouble is, anyone can change that single to a double at a later stage... you now have two doubles.
That would be their problem, it is a requirement that before alterations are made the suitability of the installation is assessed. Anyone can connect a cooker to a lighting circuit and change the fuse to a 50a, you cant blame that on the person who installed the lighting circuit.
You do know the current carrying capacity of 2.5 mm is a lot more than 13 amps, right? You can easily use a 20 amp breaker to protect a full set of double sockets on a single 2.5 mm circuit.
It is more than 13a, it is around 26a. But the idea of using a 13a FCU to fuse down a spur from a ring circuit is to prevent a potential heavy loading at one point on the ring. Rings function most efficiently when loading is evenly distributed throughout the circuit, of course in practice 2x 13a heaters could be plugged into one twin on the ring and upset that balance. But if a number of points are to be wired on a single spur it would be bad practice and non-compliant to enable a heavy loading at that point by fusing it at 20a. You are correct that a 20a breaker can be used to fuse any number of points on a single 2.5mm circuit, but that is a radial, a separate circuit, a spur off a 32a ring circuit is a completely different thing
How do you work that one out Kidsolo?You say that like it is a bad thing. Even thou I believe only one would trip.
The uk did used to have 15A and 5A unfused plugs but they went out of regular use decades ago. ( I will be corrected on that, I’m sure, as these unfused plugs are still used in some specialised places)
Dorman and Smith I believe that's the makers name utilised the fuse as the live oin on their plug tops, some of the old Council houses had them, my Mum and Dad's house had them in Bath the houses were built at or during the end of WW2The fuses are there to protect the flx of the appliance as well, which will always be less than the 2.5mm ring cable (2 x 2.5mm!)
Different fuses for different appliances.
Most common are 13A for larger appliances, and 3A for lamps, tv’s etc.
If a fault develops in an appliance, and We didn’t have a fuse in line, the flex could melt before any 32A circuit breaker senses the over current.
The uk did used to have 15A and 5A unfused plugs but they went out of regular use decades ago.
( I will be corrected on that, I’m sure, as these unfused plugs are still used in some specialised places)
This is where the problem is. We would have 20 amp breakers on each power circuit, which allows 20 or more outlets (not connected in a ring). doesn't burn out the flex before tripping the breaker. You can piggy back off other outlets, connect 3 other outlets from one. You guys made it too hard and complicated.If a fault develops in an appliance, and We didn’t have a fuse in line, the flex could melt before any 32A circuit breaker senses the over current.
This is where the problem is. We would have 20 amp breakers on each power circuit, which allows 20 or more outlets (not connected in a ring). doesn't burn out the flex before tripping the breaker. You can piggy back off other outlets, connect 3 other outlets from one. You guys made it too hard and complicated.