Hi,

Just need to check something. Sparky installed two new plug sockets. To do this, cut into the main ring, put a junction box in, one cable out to socket. Then from there connected one more plug. I understand to spur off a spur you should use a fuse between them?
 
You said not technically correct but acceptable. A two gang socket is type tested with a load of 20A (14A and 6A) across the outlets and whilst in practice this may not be the case it is fact. Based on this a two gang socket will draw no more than 20A, argue this with British Standards. Two one gang sockets have the potential to draw 26A. To apply a departure you could not guarantee a lesser standard of safety is provided by using two one gang sockets.
'Based on this a two gang socket will draw no more than 20a'!!….. Does it have a current limiter then?? A twin socket can, and will, have two 3kw 13a appliances plugged into it just the same as two singles because the plug fits both. The type testing is based on average loadings likely to be applied in average circumstances, the same average circumstances apply whether it is a twin or two singles. British Standards can say what they want, Joe Public will never ever be heard to say. " Ah, two 3kw appliances I need to use, I cant plug those into a twin because it'll only take 20a, I'd better find two separate singles to plug them into".
 
used for fusing down when you are connecting lower load
Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
 
Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
I guess it's because the UK wiring systems are the envy of the World!!
 
Sure, you are down sizing the fuse so that socket alone can't exceed 13 amps, while the rest of the circuit can. But one needs to ask "why"? Why not just use the protection set aside for the ring circuit? It is still part of the main circuit as an overall load, so why does a stray socket suddenly need it's own fuse?
and why a ring circuit? sure, it splits the load, but why not just make 2 separate circuits? you have already run the cable back to the switchboard. That way you have two separate circuits, both sharing the load of all the sockets... but you have the added advantage of only tripping one circuit at a time, instead of losing power on everything.
"Why?" only applies when the spur is to feed more than one point. A fused spur enables a single cable (2.5mm) rated at < the 32a source OCPD to feed any number of points because the load is limited to 13a. Two twin sockets on an unfused spur would have a load potential exceeding the current carrying capacity of a single 2.5mm cable which could result in thermal damage to that cable.
 
Help an Aussie understand.
The fuse connected to the spur, where is that physically situated in the installation? alongside the outlet, back in the switchboard, or somewhere else?
and do you guys still use fuses, or is that your name for a breaker?

A ring circuit has two actives in the bottom of the main breaker and two neutrals in the neutral link?
Help an Aussie understand.
The fuse connected to the spur, where is that physically situated in the installation? alongside the outlet, back in the switchboard, or somewhere else?
and do you guys still use fuses, or is that your name for a breaker?

A ring circuit has two actives in the bottom of the main breaker and two neutrals in the neutral link?
Take a look at the diagram in post 4 all will become clear
 
Two twin sockets on an unfused spur would have a load potential exceeding the current carrying capacity of a single 2.5mm cable which could result in thermal damage to that cable.
This doesn't make any sense at all. Two unfused sockets doesn't equal "unprotected", it is still protected by the 32 amp breaker (just like all the other sockets on the ring circuit). All you are doing is limiting that socket and any connected after it, to 13 amps. it is still part of the 32 amp circuit.
If two fused sockets is going to exceed the load potential of 2.5 mm, then what do you think all those other sockets going to do to the current carrying capacity of the 2.5 mm in that circuit?
 
Last edited:
The diagram clearly says "one single or one double". it doesn't say two singles equal one double
It doesn't, and I never said Bs7671 says two singles equals one double. I said in my opinion there is no difference in practice because both allow the connection of any two 13a appliances with a 13a plug.
This doesn't make any sense at all. Two unfused sockets doesn't equal "unprotected", it is still protected by the 32 amp breaker (just like all the other sockets on the ring circuit). All you are doing is limiting that socket and any connected after it, to 13 amps. it is still part of the 32 amp circuit.
If two fused sockets is going to exceed the load potential of 2.5 mm, then what do you think all those other sockets going to do to the current carrying capacity of the 2.5 mm in that circuit?
You are completely missing the point. A ring is protected by a 32a breaker because each socket on the ring is effectively fed by TWO 2.5mm cables, not one. If you reduce the supply cable to ONE 2.5mm with a spur off the ring then the load carrying capacity of that part of the circuit is effectively halved, it's no longer capable of carrying 32a. That's why the spur cable would need to have a reduced overcurrent device to protect only the spur if it supplies more than one twin outlet.(or more than one single to be in compliance with the guidance in 7671.
 

Reply to Spur off spur in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
441
  • Question
It can be easy to lose the sequence of things. If the fused spur has a neon indicator and this isn’t coming on then I wonder if -the original...
Replies
6
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top