I had a problem with a ring main it kept tripping out
The electician found a fault between 2 sockets so broke the ring as wires in wall and running under bathroom floor
The cable is 2.5
When i have my drier running and switch on kettle it trips out how can i change this
No idea about electrics
 
from what i can glean from posts. the electrician has split a faulty ring into 2 radials, down rated the MCBs (as he should), but now there's too much load being put onto 1 of the circuits. moving a heavyload like a kettle to a different circuit eliminates the problem, but at the end of the day, the fault should have been found, fixed, and the ring reinstated. even if demolition of some of the building fabric was necessary. that's why we tolerate builders, plasterers and paint splodgers. got to keep the buggers off the dole.
Thanks for everything am definitely going to reinstate ring main which
will be done between tenants
Could the ring main be fixed by trunking a cable between the 2 sockets they are both halfway up the wall
either side of back door
Could i check if ring will work by plugging into both sockets with a 2.5 cable or are the fuses all wrong
Sorry no idea what i am talking about
I presume it was a bigger fuse when it was ring to what i should have now on 2 radials and so it will be changed back when change back to ring
l am only thinking that he added another fuse not definite but moving kettle would not make a difference i presume if that was case
 
There's nothing inherently wrong with what your electrician has done, AS LONG as he has connected the two radials onto two separate MCBs, the split in the ring isn't too close to one end of the original ring, the abandoned section of the ring has been totally disconnected at both ends, and the original (presumably) 32A MCB has been replaced by a 20A one, along with a second 20A MCB for the 'new' circuit.
This will allow a higher load to be connected in the kitchen than before, but it will need to be distributed between the two radials.
A well designed RFC (ring) should have been arranged so that the expected significant loads were distributed so as to not load one half above the rating of the cable.
 
Thanks for everything am definitely going to reinstate ring main which
will be done between tenants
Could the ring main be fixed by trunking a cable between the 2 sockets they are both halfway up the wall
either side of back door
Could i check if ring will work by plugging into both sockets with a 2.5 cable or are the fuses all wrong
Sorry no idea what i am talking about
I presume it was a bigger fuse when it was ring to what i should have now on 2 radials and so it will be changed back when change back to ring
l am only thinking that he added another fuse not definite but moving kettle would not make a difference i presume if that was case
WEST hOUGHTON is within reach of my shark teeth. if and when you want it fixing reet, pm me.
 
I’ve redacted your information. Will ask a mod to remove yours.

[ElectriciansForums.net] RING/RADIAL
 
The way I’m reading it, there’s only one ring circuit with 23 points. If this is the one at fault, and it’s been split.... at the extreme there could be 1 point on one new radial and 22 off the other.

if question why the rcd test buttons haven’t been tested. Marked N/A
 
Ok there's something wrong there then as the schedule of test results just shows one circuit for sockets, no end to end results showing the circuit is no longer a ring and it's on a 30 amp breaker. Not great.
 

Reply to RING/RADIAL in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
610
  • Question
Why aren't you asking them?
Replies
5
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top