I had a problem with a ring main it kept tripping out
The electician found a fault between 2 sockets so broke the ring as wires in wall and running under bathroom floor
The cable is 2.5
When i have my drier running and switch on kettle it trips out how can i change this
No idea about electrics
 
The M bit is the maximum breaking capacity of the MCB in 1000s of amps, and is not normally a consideration in domestic premises. Modern domestic versions are usually M6.
The 'type 2' bit refers to the ratio of instant trip current (short circuit) to overload trip current, and type 2 is what you want.
As long as the position of the connection to the busbar matches the existing ones the 'M' rating doesn't really matter, as long as it's equal or greater to than the PSC current shown on your EICR.
 

Reply to RING/RADIAL in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
610
  • Question
Why aren't you asking them?
Replies
5
Views
816

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top