I’ve been looking for the right answer and just can’t seem to find it.
I had an induction hob installed by a certified electrician, and there are no apparent problems so far, however, it is installed on the CU, RCD and upstream with a RCCB with no MCB,
I’m just not 100% sure if it’s the safest way to install it, I would personally think that would be safer on an RCBO or on a MCB, I’m not worried about overloading as it’s on a 10mm2 cable, 40a RCCB and the unit draws a max of 25Amp, I worry more about the fact that the RCCB will not protect on short circuit.
I appreciate any feedback or comments.
Thanks
 

Attachments

  • [ElectriciansForums.net] Induction hob correct install
    9683AA16-5980-4207-88CA-83C96C6EF8C1.jpeg
    557 KB · Views: 122
Can't be certain but it appears the RCCB is fed from the top left 32 amp MCB.
That board is a bit of mess to say the least.
Thanks for the comment, yes not state of the art.. it’s a 20 years old CU. The RCCB is feed from the busbar from the RCD as all the other MCBs on the busbar, I think there is no problem there. Question is about the RCCB being safe or not without an MCB.
Thanks
 
Thanks for the comment, yes not state of the art.. it’s a 20 years old CU. The RCCB is feed from the busbar from the RCD as all the other MCBs on the busbar, I think there is no problem there. Question is about the RCCB being safe or not without an MCB.
Thanks
In that case, the circuit fed from the RCCB has no overcurrent protection.
 
OP, what made you look at how the electrician had wired the cooker into the consumer unit?

Did you get an installation cert?

And yes, fundamentally every circuit needs over current protection of some sort.
my interest and curiosity for electricity and the safety of my home and family, do that suffice?
no cert provided..... cowboy, I called many snags on the electrician alone... I'll spare you the details, just to say the cover for the connection under the hob was found on a drawer... then I saw the wires exposed...
 
Thank you all for your comments, very much appreciate that you took your time to give your opinion on what seems to be a hot mess of a CU, I kind of knew that, the whole house was built on a weekend during the boom in Ireland so no surprise there. I just want to focus on having the correct protection, for now, aesthetics is not my main concern right now.
What I take from all your comments is that the RCCB where the Induction hob is should be an RCBO, and that the current RCCB does not provide enough protection to the hob or the circuit and it could be an electrical hazard?
 
On the face of what is presented above I would say the OCP is not achieved with the installation method used. What might be the consequences of this? In terms of overload it is not a problem as it is a fixed resistive load and can only achieve a fixed amount of load. In the event of a short circuit where the load may well exceed the CCC of the cable due to the fault current exceeding by many multiples the CCC of the cable. Therefore the cable may melt/explode causing danger of fire. It would then be prudent and indeed required to arrange the appropriate protection for the cable. Ensuring the operative engaged is properly qualified to undertake such work. The chance of a short circuit while being quite remote is nevertheless important to have remedied.
 
On the face of what is presented above I would say the OCP is not achieved with the installation method used. What might be the consequences of this? In terms of overload it is not a problem as it is a fixed resistive load and can only achieve a fixed amount of load. In the event of a short circuit where the load may well exceed the CCC of the cable due to the fault current exceeding by many multiples the CCC of the cable. Therefore the cable may melt/explode causing danger of fire. It would then be prudent and indeed required to arrange the appropriate protection for the cable. Ensuring the operative engaged is properly qualified to undertake such work. The chance of a short circuit while being quite remote is nevertheless important to have remedied.
thank you very much for your comments and advice, much appreciated.
I've decided to keep the RCCB turned off while not in use just in case.
I will make sure a reputable certified electrician does the job... possibly replacing the whole CU and new more modern type B breakers with 6ka capacity class3, instead of 3ka, although here in Ireland that it's extremely hard! not to say almost an impossible quest!
 
Thank you, I'll consider that, in the main time if my electrician suggests adding an MCB to the RCCB instead of replacing it with an RCBO, where should the electrician position the MCB, before the RCCB or after connected to the load?
thanks
Ideally between the RCD and the load - as is the case with the lower Hager RCD. That way the MCB protects the RCD against the effects of a short circuit (Though in this case with one load it may not make much practical difference.)

In either case it should really be a short term solution until you can get the whole installation looked at. Some of the Hager stuff looks in good condition and is still 'current' so it may be possible to reuse them, perhaps in a new enclosure depending on the state of the existing one, add some Hager Type A RCBOs on relevant circuits and end up with a much better installation without massive time or cost involved.
 

Reply to Induction hob correct install in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
The OP is in New Zealand
Replies
3
Views
1K
davesparks
D
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K
Hi there, I'm facing the same issues with my Ikea Blixtsnabb (a rebranded Electrolux / AEG model) and wondering if I can achieve the same thing to...
Replies
9
Views
6K
  • Question
A socket-outlet could be connected to one of those circuits using 2.5mm² or as PC1966 says, even 1.5, although I personally would use 2.5 because...
Replies
6
Views
3K
  • Question
Hi I really cannot give you an answer if you need 2391 to do your own jobs, however I do know to get into an inspection council they ask for...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks