Open end to end readings on ring main on rn r2 - where should this go under in schedule of inspections
using napit software doing a DEICR
C2?
 
There is no specific observation for ring circuit continuity.

You could maybe use "connections soundly made..." Under. 5.17.

Reg. 643.2.1 applies.
 
It's not the result of an inspection but of testing so the Schedule of Inspections isn't relevant to the observation.
 
im on the napit fast test certificate so doesnt show that
Ah ok. Have you got:
5.5 Adequacy of cables for current-carrying capacity with regard for the type and nature of installation (Section 523)

As effectively you have two undersized radials hanging off a B32.
 
The fault has been identified as warranting a C2.
No further investigation required.
Future fault finding with a view to correcting a fault is not the same thing as FI.
Valid point, and i see where you're coming from. ?
 
Valid point, and i see where you're coming from. ?
I was also reminded of this yesterday, focussing on coding the fault not the fix seems to make it clearer in my befuddled brain...
(In my case high Zs on lighting circuit at every point)
 

Reply to Open end to end on rn r2 - where should this go under in schedule of inspections? in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
358
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
326
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
369

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top