Hi All.
I've got to get a job ready for Pod point to install a car charging unit.
They need the gas bonding to be done,which is quite straight forward.
And they need a type A RCD put in the board.
The point is going in a garage which has a sub board feed from a B40 mcb on the main house board,which has type AC RCDs.
Im finding it difficult to get hold of more specific information from them. But Im guessing they want the AC RCD covering the B40 mcb in the main board swapping out for a type A ?
Should the subboard also have a type A RCD?
I've only briefly visited the job,so I still have to get my bearings with it all.
Any thoughts from those that know more than me on this?
 
DC-sensitive type B RCDs are quite expensive, check if it is actually needed as some EV chargers only expect type A feeding them as they handle DC leaks themselves.

If the main board has a 30mA RCD feeding the garage then it does not need a local RCD. It won't do any harm, but it is not needed, and means there are two possible devices to reset if tripped.

If the garage feed is SWA then it does not need a RCD feeding it (unless TT so Ze too high) so it would be better to have the RCD at the garage CU and a non-RCD MCB on the supply. Less chance of a garage/EV fault taking out house electrics.
 
DC-sensitive type B RCDs are quite expensive, check if it is actually needed as some EV chargers only expect type A feeding them as they handle DC leaks themselves.

If the main board has a 30mA RCD feeding the garage then it does not need a local RCD. It won't do any harm, but it is not needed, and means there are two possible devices to reset if tripped.

If the garage feed is SWA then it does not need a RCD feeding it (unless TT so Ze too high) so it would be better to have the RCD at the garage CU and a non-RCD MCB on the supply. Less chance of a garage/EV fault taking out house electrics.
Brilliant thanks , they have stipulated a type A rcd .
 
Just to add, if you can change the board RCD to type A it is generally a good thing as better protects other circuits from electronic-style faults.

But see what you find on a closer inspection. You might also find problems in getting new parts for it if the main board is quite old which makes the best solution a more complicated judgment.

If in doubt get some photos, @westward10 is the one to ask for any unusual CU parts, he is a walking encyclopedia!
 
Just to add, if you can change the board RCD to type A it is generally a good thing as better protects other circuits from electronic-style faults.

But see what you find on a closer inspection. You might also find problems in getting new parts for it if the main board is quite old which makes the best solution a more complicated judgment.

If in doubt get some photos, @westward10 is the one to ask for any unusual CU parts, he is a walking encyclopedia!
Thank you very much for taking the time. Much appreciated ?
 
If the Sub main is SWA remove from DB and fit in switch fuse sized to cable size etc and feed from Tails with Henry's

Garage end fit a new DB with Separte DP RCBO for each circuit Pod point will fit a CT to garage supply and set the clamp current to the size of the switch fuse or lower to stop any overloads of the sub main

Any questions PM me as quite knowledgeable on there use and installation

And a type A RCBO is fine if you have a AC downstream it will be Blinded by the DC and might not work so essential to get this right
 
If the Sub main is SWA remove from DB and fit in switch fuse sized to cable size etc and feed from Tails with Henry's
Sorry, but can't get this image out of head now...
Like this?
[ElectriciansForums.net] Type A RCD upstream,downstream or up the swanny.
 
Last edited:
Fit an MCB in the garage board and route it through a separate type a rcd?
Typical Pod Point though... get all the hard work done as they cant and dont do it then come fit a charger...
I use the small enclosures with Type A RCD/RCBOs in from WCED you can buy one on amazon for £25-30
 

Reply to Type A RCD upstream,downstream or up the swanny. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Thanks Westward, and that last paragraph with the Note about no characteristic marking is exactly what I needed to see.
Replies
2
Views
503
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
721

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top