Hi,

I have an aico alarm system which was mains powered and interconnected when installed 3 years ago. It's not been maintained and when I took a look recently, a couple of the detectors are missing. Only the ceiling plate is on the ceiling. Also, the interconnect isn't working. When I test any smoke detector, only that beeps and - none of the others.

I need to ensure that they are all still mains powered and restore the interconnection between them. They have a 3 core and earth cable for the interconnect.

I am pretty handy with electrics and own various tools including a fluke 2 pole tester.

I have 8 detectors. Can you please suggest a logical approach for this. Does the indicator on the detectors have any significance?

Look forward to receiving your advice. Thanks in advance.
 
I think the Aico call points look like 3 switches??. Like a remote test button?. Never wired one, so i dont know.




quick google: Is this it?
[ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
 
In terms of testing the cabling there are two separate tests that need doing :

1) Check that (with all the heads removed) there is no connection between any of the four wires (including earth). If (say) the interconnect was shorted to the neutral then the interconnect wouldn't work and you'll get the symptoms described (only the one unit will sound).

2) Check that there's a complete link along each - i.e. L, N, and interconnect is connected between all the bases. As already said, if there's a break in the interconnect then the units will work in separate groups - those one side of the break, and separately the ones the other side of the break.

And for this size on installation, there really should be a test/isolate switch which for a hardwires system would be the one littlespark posted a photo of in post #76.
 
Last edited by a moderator:
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
 
As an observation rental properties should not have battery backed ionisation alarms fitted , should be optical with built in rechargable battery ie:3016 from AICO , this applies in hallways and general living spaces , heat alarm in the kitchen , ionisation are acceptable in bedrooms.
Where does it state this? I was advised by the local authority to fit a mains powered interconnected system. There was no additional stipulation.
Can you clarify please.
 
Wouldn't surprise me if he's also right on the requirement for mains +rechargeable

That's the way it should be for rented accommodation, as near as possible to a maintenance free system

So what the council are now requiring here(Eire) when leasing property for rental is a fire panel fitted , seems like overkill but...
 
So "recommended", not "mandatory". But I'd not user user-replacable batteries anyhow - to tenants they are either a nuisance that can be silenced by removing the battery, or a handy spare battery for something else ?
Can you silence them by removing the battery alone , don't think so ?

What they will do is slide off the whole lot and take out the battery
 
Aico 141 and 146 smoke alarms will be silenced if you remove them from their base. This disconnects both the mains supply and the battery.
If the alarm is refitted without the battery it will still do what it's designed for, but will emit an annoying single bleep every couple of minutes, the same as with a failing battery.
Most common cause of removed Aico 146 alarms is false sounding because of dust in the optical chamber.
 
Aico 141 and 146 smoke alarms will be silenced if you remove them from their base. This disconnects both the mains supply and the battery.
If the alarm is refitted without the battery it will still do what it's designed for, but will emit an annoying single bleep every couple of minutes, the same as with a failing battery.
Most common cause of removed Aico 146 alarms is false sounding because of dust in the optical chamber
They're supplied with battery connected ,so stands to reason you can just whip off the head to silence it , if im getting it right

Was assuming first you'd also have to remove alkaline battery, I should probably remember
 
UPDATE: I created a test rig with two new smoke alarms. I connected them together using 3 core and earth - on the ground (powered by 9v battery) and as expected, the interconnect works with them. I then removed one of the new heads from this set-up and replaced it with each of the 8 heads currently in the house. I tested each of them in both directions: tested the new alarm and the head from the house. None of them apart from one provided the interconnect. They all worked independently. I concluded that 7 of the detectors were faulty.

I purchased 7 new alarms, popped them on one device after the other whilst testing them. They all work!
I did inspect the wiring on each detector and it seemed fine.

I did notice that one of the bases had a burn mark. I replaced this base but with all other detectors, I retained the old bases and slid on the new heads.


All the faulty detectors had a "Replace By" date of June 2026.


I have written to Aico to see if they can cover any of the cost but unfortunately, I don't have receipts for the old detectors.

Here are some images of the call point:

I am questioning whether there is any benefit in having a key for this as it's just as easy to test the system from any of the detectors.

Interested in your thoughts on the above and also, what may have caused the issue which led to all the interconnects failing. Since I have not changed anything other than fitting the new heads, could the underlying issue still be there? Also, is there any reason to retain or fit the bases that came with the new detectors? I left the old bases apart from the one that had a burn mark.

Can I also take this opportunity to thanks everyone for their help and advice.
 

Attachments

  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232689286.png
    625.3 KB · Views: 14
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232799819.png
    502.7 KB · Views: 14
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232799087.png
    1.3 MB · Views: 12
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232894012.png
    745.8 KB · Views: 13
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232894423.png
    502.7 KB · Views: 13
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232894895.png
    1.1 MB · Views: 10
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232947037.png
    552 KB · Views: 17
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232946811.png
    502.7 KB · Views: 10
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232946445.png
    1 MB · Views: 10
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232947356.png
    1.1 MB · Views: 14
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232987222.png
    502.7 KB · Views: 16
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232987416.png
    552 KB · Views: 12
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232987874.png
    787.2 KB · Views: 9
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232988294.png
    1.1 MB · Views: 12
  • [ElectriciansForums.net] Interconnected smoke alarm - troubleshooting
    1636232986708.png
    1.6 MB · Views: 11
On a system that size you really need a test switch - otherwise if there's an alarm, you'll be chasing round trying to find the one that's triggered, while being deafened by the racket. With the test switch, you can press the locate switch and all but the one that triggered will turn off.

And of course, if it's rented then tenants (even ones you thought were good ones) will be quite ready to remove what they consider to be "faulty" alarm heads. And since they probably aren't familiar with the little details, they might not use the slot to release the slide lock - so next time you do an inspection you find that the base is broken as well as the head missing. Guess how I know that ?
 
On a system that size you really need a test switch - otherwise if there's an alarm, you'll be chasing round trying to find the one that's triggered, while being deafened by the racket. With the test switch, you can press the locate switch and all but the one that triggered will turn off.

And of course, if it's rented then tenants (even ones you thought were good ones) will be quite ready to remove what they consider to be "faulty" alarm heads. And since they probably aren't familiar with the little details, they might not use the slot to release the slide lock - so next time you do an inspection you find that the base is broken as well as the head missing. Guess how I know that ?


I’m pritty sure the locate function only works if it is a rf system
 
You can mix and match with the Aico stuff. In our rental flat we have one sensor and the switch wired, two more sensors wired, and radio modules in two sensors to bridge the two wired segments.
Operting the test switch makes its hardwired head sound immediately - then a couple of seconds later the other two heads sound.

What you don't get on a wired setup (but do with radio) is having all the sensors sound according to the function that triggered. E.g. a Heat & CO head will make different sounds depending on what triggered it. In a radio linked setup, all the other heads will copy that. But with wired interlink they just do their default sound.
 

Reply to Interconnected smoke alarm - troubleshooting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
That explanation would make a lot of sense and would certainly explain the new bases and new boxes, with old relabelled alarm heads. I do remember...
Replies
5
Views
571
I really don’t see why you can’t do that. So have your electrician to take loose the wiring that the solar person did for you. He can now come off...
Replies
4
Views
2K
  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
639
  • Question
As @UNG said, there can be long delays in obtaining alarms, especially from Aico. I had this problem when the new Scottish regs came into play...
Replies
12
Views
2K
  • Question
Thank you, that's a really helpful post, nice & clearly stated and helps me clear up a lot of confusion on this matter.
2 3
Replies
65
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks