Thanks Julie , he has quoted £1000 to do all the work so wanted to ask for some advice on here .

Also can you explain what do you mean by socket within 3m of zone 1 . Should it be more than 3m away ?
When you have a bath or shower, the space around is defined by zones 0, 1 & 2, and there are different requirements for ingress protection (waterproofness), types of equipment etc for each zone.

There is also a regulation which prevents having a standard socket outlet within 3 metres.

However this only applies within the room itself, or if there isn't a barrier (door, window, hatch etc).

So you can have an outlet directly outside the bathroom door for example, but if you remove the door then it would be prohibited.

If the shower is contained within a proper enclosure (not just a leaky cubicle), again ok within 3 metres, (but not within zone 2), remove the shower enclosure then prohibited etc.

[ElectriciansForums.net] failed EICR, please can you advice
 
Just to add that the report says:
"Low voltage (e.g. 230 volt) socket-outlets sited at least 3 m from zone 1 (701.512.3) Fan isolation switch in bathroom and on-suite. x2 in total"
The first section was auto-completed from ticking a box elsewhere. I still think it actually refers to having fan isolators in zone 2. The "socket" could be a complete red herring, due to the wrong schedule item being chosen.
 
Just to add that the report says:
"Low voltage (e.g. 230 volt) socket-outlets sited at least 3 m from zone 1 (701.512.3) Fan isolation switch in bathroom and on-suite. x2 in total"
The first section was auto-completed from ticking a box elsewhere. I still think it actually refers to having fan isolators in zone 2. The "socket" could be a complete red herring, due to the wrong schedule item being chosen.
I agree but if these isolators are in zone 2 it wouldn't matter if they are waterproof, whatever that is or sprinkled with fairy dust they shouldn't be in zone 2. The report however isn't clear where they are and outside of this zone they can be standard isolators.
 
I agree but if these isolators are in zone 2 it wouldn't matter if they are waterproof, whatever that is or sprinkled with fairy dust they shouldn't be in zone 2. The report however isn't clear where they are and outside of this zone they can be standard isolators.
Agreed. It's definitely not an optimal write up...
btw the 'waterproof' thing was about lights and sockets under the kitchen sink - different items.
 
Agreed. It's definitely not an optimal write up...
btw the 'waterproof' thing was about lights and sockets under the kitchen sink - different items.
It mentions waterproof isolators in #1. The house will end up looking like a plant room😂😂
 
It mentions waterproof isolators in #1. The house will end up looking like a plant room😂😂
Ah - I was looking at the report itself which is a bit (but not much!) clearer than the paraphrased version from the landlord.
 
I'm well aware of that, but it's the kind of thing that gives rise to spurious coding on EICRs - the subject of this thread.
Do a google image search for "bathroom zones", and 18 of the first 20 results show one!
It takes concerted effort to find a correct diagram unfortunately.
 
Do a google image search for "bathroom zones", and 18 of the first 20 results show one!
It takes concerted effort to find a correct diagram unfortunately.
The 60cm seems quite specific though, is that some general guidance for sinks instead of bathroom-specific zones?
 
The 60cm seems quite specific though, is that some general guidance for sinks instead of bathroom-specific zones?
There's nothing specific in BS7671. There are a few documents that mention 30cm, e.g. NHBC technical notes, GN1, and those fine fellows upholding the standards of the industry at NICEIC...

Section 512.2 has only general comments for the external influence of Water.
 

Reply to failed EICR, please can you advice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

I think it is a good idea in general, it provides a form of proof that the landlord has provide access to the required documents. further to that...
2
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top