I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet room has basically rotted away over 5 years, it has now been completely removed by another firm and is in the process of being redone.

The work by the company being investigated involved changing a shower room into wet room. I.e a completely waterproofed shower room space.

The electrical work that the company installed was as follows. Would you agree with codes?

1. Installed an IP45 extractor fan in zone 1 (see picture) - No code
2. Installed an RCD fused spur just the other side of the partition (for fan). You could in theory reach over the partition and touch the switch - C2 (This would be zone 2 IF we don't class there as being a partition - see 'further points' below)
3. Installed 2 x switched FCU's approx 60mm away from partition - could in theory get sprayed from shower - C2
4. Put washing machine and tumble dryer just the other side of partition, meaning they are in zone 2 (or zone 1 if partition not classed as partition (see picture) - C2

Further points

The partition is in place, but it is not very high. The diagram in OSG shows the partition reaching the ceiling. So perhaps I do not even class this as a partition? Is it a permanent fixed partition?

The consumer unit had some C2's. Are we responsible for this if we are adding to the electrical installation even though we are not working on the consumer unit?

The bathroom lights are just outside the zones (2.27m high). They are not IP rated but they are ELV. They are not fire rated and there is living space above. Any codes here? These lights are not IP rated so (even though they are ELV) would they be suitable for location. The company did not install the lights.

There is one ELV MR16 light just the other side of the partition which would be in zone 2 if the partition is not classed as a partition. Again not IP rated.

lastly, the bathroom lights have no RCD protection. Does this mean there should be supplementary bonding to the towel radiator from one of the circuits in the location? In theory they could touch one of the ELV lights and radiator at the same time. I believe supplementary bonding would be required as it does not meet the requirements for omission in 701.415.2

Cheers all 🙂

[ElectriciansForums.net] What are you responsible for when carrying out electrical work?
 
The consumer unit had some C2's. Are we responsible for this if we are adding to the electrical installation even though we are not working on the consumer unit?

IMO, you are only responsible for the circuits you are altering or adding.
If the CU is not up to scratch then this should be sorted before altering or adding extra circuits.
 
IMO, you are only responsible for the circuits you are altering or adding.
If the CU is not up to scratch then this should be sorted before altering or adding extra circuits.
Many would agree...but i am of the opinion anything related that worries me gets discussed with the client and noted
 
Many would agree...but i am of the opinion anything related that worries me gets discussed with the client and noted

That's where my second sentence comes into play. Nothing in the CU should worry you and the CU should be safe.
 
IMO, you are only responsible for the circuits you are altering or adding.
If the CU is not up to scratch then this should be sorted before altering or adding extra circuits.
Many would agree...but i am of the opinion anything related that worries me gets discussed with the client and noted
I agree, but seeing as though this is for trading standards i need to give facts, not opinions.
Any reg numbers for being responsible for the CU once work has been carried out elsewhere?
 
1. Installed an IP45 extractor fan in zone 1 (see picture) - No code
2. Installed an RCD fused spur just the other side of the partition (for fan). You could in theory reach over the partition and touch the switch - C2 (This would be zone 2 IF we don't class there as being a partition - see 'further points' below)
3. Installed 2 x switched FCU's approx 60mm away from partition - could in theory get sprayed from shower - C2
4. Put washing machine and tumble dryer just the other side of partition, meaning they are in zone 2 (or zone 1 if partition not classed as partition (see picture) - C2
Your coding seems about right to me.
The partition is in place, but it is not very high. The diagram in OSG shows the partition reaching the ceiling. So perhaps I do not even class this as a partition? Is it a permanent fixed partition?
I would say so, it limits zone 1. It's not like anyone can move it without getting the tool kit out.
The consumer unit had some C2's. Are we responsible for this if we are adding to the electrical installation even though we are not working on the consumer unit?
Hard to say, what were the C2s?
The bathroom lights are just outside the zones (2.27m high). They are not IP rated but they are ELV. They are not fire rated and there is living space above. Any codes here? These lights are not IP rated so (even though they are ELV) would they be suitable for location. The company did not install the lights.
No code - out of zones, and no danger as ELV (EICRs are AFAIK only coded for safety, please somebody correct this if I'm mistaken)
There is one ELV MR16 light just the other side of the partition which would be in zone 2 if the partition is not classed as a partition. Again not IP rated.
No code, no danger as ELV.
lastly, the bathroom lights have no RCD protection. Does this mean there should be supplementary bonding to the towel radiator from one of the circuits in the location? In theory they could touch one of the ELV lights and radiator at the same time. I believe supplementary bonding would be required as it does not meet the requirements for omission in 701.415.2
No. Supplementary bonding is required for ADS, and ELV isn't ADS (ie the metal parts of ELV lights aren't exposed conductive parts)
 
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet room has basically rotted away over 5 years, it has now been completely removed by another firm and is in the process of being redone.

The work by the company being investigated involved changing a shower room into wet room. I.e a completely waterproofed shower room space.

The electrical work that the company installed was as follows. Would you agree with codes?

1. Installed an IP45 extractor fan in zone 1 (see picture) - No code
2. Installed an RCD fused spur just the other side of the partition (for fan). You could in theory reach over the partition and touch the switch - C2 (This would be zone 2 IF we don't class there as being a partition - see 'further points' below)
3. Installed 2 x switched FCU's approx 60mm away from partition - could in theory get sprayed from shower - C2
4. Put washing machine and tumble dryer just the other side of partition, meaning they are in zone 2 (or zone 1 if partition not classed as partition (see picture) - C2

Further points

The partition is in place, but it is not very high. The diagram in OSG shows the partition reaching the ceiling. So perhaps I do not even class this as a partition? Is it a permanent fixed partition?

The consumer unit had some C2's. Are we responsible for this if we are adding to the electrical installation even though we are not working on the consumer unit?

The bathroom lights are just outside the zones (2.27m high). They are not IP rated but they are ELV. They are not fire rated and there is living space above. Any codes here? These lights are not IP rated so (even though they are ELV) would they be suitable for location. The company did not install the lights.

There is one ELV MR16 light just the other side of the partition which would be in zone 2 if the partition is not classed as a partition. Again not IP rated.

lastly, the bathroom lights have no RCD protection. Does this mean there should be supplementary bonding to the towel radiator from one of the circuits in the location? In theory they could touch one of the ELV lights and radiator at the same time. I believe supplementary bonding would be required as it does not meet the requirements for omission in 701.415.2

Cheers all 🙂

View attachment 95739
Anything you touch, alter etc I would think, of course if you are a switch on Bang merchant nothing
 
Are they asking you to carry out a Report or an EICR. When I have done this sort of thing they want a factual report not an EICR.
oo, interesting, could you explain a little more the difference please Westward?

I think it is more 'me' that has suggested an EICR on the wet room, as I didn't realise there was anything else.
 
At first look it doesn’t look great.

Your point 3… you say 60mm… is that right or do you mean 600? Which takes it to the next zone.

I wouldn’t class a shower screen as a partition. Although a thin frame with a bit of wet wall panelling doesn’t sound much more substantial.

A lot of kitchen/bathroom fitters will just fit an rcd spur to cover their work, and never even look at the db except to switch it off and on again.
Was any testing done? Certs available?

Is the light ELV, or SELV?


I think you might just have to do an EICR just for the affected circuits as you normally would, then write a page or two to elaborate on the specific problems.
Maybe avoid words like “should” and “must” and go with “may” on your report.

If TS are trying to get the company prosecuted, then your report will be evidential.
Can you honestly say what they did was against the regs at the time? Or their understanding of the regs regarding what a “partition” is?
.
 
oo, interesting, could you explain a little more the difference please Westward?

I think it is more 'me' that has suggested an EICR on the wet room, as I didn't realise there was anything else.
Not done it for a while and your case differs somewhat as no one has died or claimed to have received an electrical shock. Reports I have done have been house fires, death from electrocution and people who have claimed to have received a shock in factories, the latter often chancers but in one instance they had a genuine claim. In your situation the fact things have 'rotted away' is irrelevant to the electrical installation so they are looking for an expert opinion to reinforce the claim over their incompetence. Personally I would compile a written report citing departures from BS7671, they don't want chapter and verse just facts and the possible consequences of these departures. You really need to know what they are expecting from you.
 
Not done it for a while and your case differs somewhat as no one has died or claimed to have received an electrical shock. Reports I have done have been house fires, death from electrocution and people who have claimed to have received a shock in factories, the latter often chancers but in one instance they had a genuine claim. In your situation the fact things have 'rotted away' is irrelevant to the electrical installation so they are looking for an expert opinion to reinforce the claim over their incompetence. Personally I would compile a written report citing departures from BS7671, they don't want chapter and verse just facts and the possible consequences of these departures. You really need to know what they are expecting from you.
Thankyou Westward, that's really helpful.
 
If you are going to do something like this you must be 100% confident in what you are quoting but as I say you really need to know what they want.
 

Reply to What are you responsible for when carrying out electrical work? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
181
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
556
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
515

Similar threads

  • Question
It's actually not as those are accidents outside of work, if you suffer an injury whilst working for someone else or doing private work then...
Replies
12
Views
1K
davesparks
D
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
814

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top