loz2754
Regarding the fixed partition -
The shower has no basin, therefore zone 1 extends to 1.2 metres from the fixed water outlet and further out from the partition (there is no zone 2)
as shown in the diagram on page 243 of the wiring regulations:
701.55 Current-using equipment -
In zone 1, the list of permitted equipment includes ventilation (fans), but not washing machines and tumble dryers.
The shower has no basin, therefore zone 1 extends to 1.2 metres from the fixed water outlet and further out from the partition (there is no zone 2)
as shown in the diagram on page 243 of the wiring regulations:
701.55 Current-using equipment -
In zone 1, the list of permitted equipment includes ventilation (fans), but not washing machines and tumble dryers.