I have 3 double sockets all fed from separate 32 AMP EACH . The distance is 2m from the board and the cable is in 25mm metal conduit.
I have used 4mm single core cable for each socket . I’m told I need to upgrade this to 6mm single core . Why is 4mm not big enough ??

(reason it’s single is so each socket is independent due to what gets used in them CANT have all appliances off at once,just incase or I would have a ring)
 
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
 
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
Why am I being told it need upgrade to 6mm ?
 
Maximum current rating for a double 13A socket is 20A. Even if you overload the socket by drawing 13A from each side at the same time, that is still only 26A, therefore 4.0mm2 is adequate. If the 20A loading was respected, then 2.5mm2 would be adequate, as it is for a socket spurred off a RFC protected by a 32A MCB.
I’m told the table says MAX is 30 for 4mm in conduit . Cause it’s a 32 then 6mm Is needed . Is this right
 
This is Table 4D1A of BS7671.
[ElectriciansForums.net] Need some advice please
 

Reply to Need some advice please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
532
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
  • Solved
Please use the like button to thank, like or whatever. As the forum treats that as a positive message then and uses it to score members.
    • Optimistic
Replies
11
Views
865
  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks