Hello everyone,

I have a goldsmith oven to which I had to change an SSR relay because when it reached 475 degrees centigrade the temperature increase stopped. Since the oven must reach 800 degrees in about two hours, I have to solve the problem.

I changed all the main components to the oven: thermoregulator, thermocouple, resistance. The problem of increasing the temperature was present even before changing all these components.

I ordered an SSR relay of the same brand and model as the one mounted on the oven: Crydom D2425.

Since it was panel mounted I proceeded to modify the panel to put a heatsink in it.

Between the heatsink and the relay I put some Thermalright TFX thermal paste which has a high thermal conductivity power and is also used in computers and can withstand up to 300 degrees.

After having reassembled everything I turned on the oven, this time it reached 100 degrees centigrade after 10-15 minutes the increase in temperature stopped.

I wonder where he went wrong about the SSR relay changing as I think I've done everything possible. Could anyone help me? Thank you in advance for your reply.

I attach some photos to the message.
 

Attachments

  • [ElectriciansForums.net] SSR relay problem solution
    vecchio_pannello.jpg
    74 KB · Views: 55
  • [ElectriciansForums.net] SSR relay problem solution
    nuovo_relay_pannello_sx.jpg
    369.2 KB · Views: 42
  • [ElectriciansForums.net] SSR relay problem solution
    nuovo_relay_pannello_dx.jpg
    144.3 KB · Views: 47
  • [ElectriciansForums.net] SSR relay problem solution
    relay_nuovo_con_dissipatore.jpg
    258.1 KB · Views: 42
  • [ElectriciansForums.net] SSR relay problem solution
    relay_nuovo.jpg
    104.6 KB · Views: 36
  • [ElectriciansForums.net] SSR relay problem solution
    dissipatore_pasta_termica.jpg
    190.2 KB · Views: 51
  • [ElectriciansForums.net] SSR relay problem solution
    vecchio_relay.jpg
    147.3 KB · Views: 40
In the input of the relay and at the output of the rectifier bridge the measured direct current is 22.6 volts. When the heating process is on, the DC current measured at the SSR input is 22.3-22.4v instead when the heating process is off, it is approximately 22.6-22.8v.



So to be clear - the voltage across the ssr terminals 3 and 4 is always in the range 22.3 - 22.8 V? It never drops to zero Volts even when the heating process is Off? This is surprising and not what one would expect.

Why will you not connect the SSR to the controller's SSR output? This output is designed to switch the SSR on and off.

Could you draw a diagram of how items are connected please?
 
So to be clear - the voltage across the ssr terminals 3 and 4 is always in the range 22.3 - 22.8 V? It never drops to zero Volts even when the heating process is Off? This is surprising and not what one would expect.

Why will you not connect the SSR to the controller's SSR output? This output is designed to switch the SSR on and off.

Could you draw a diagram of how items are connected please?
Yes, it is always in that range even when the heating is not on.
I can't fully understand how the oven works.
 
So to be clear - the voltage across the ssr terminals 3 and 4 is always in the range 22.3 - 22.8 V? It never drops to zero Volts even when the heating process is Off? This is surprising and not what one would expect.

Why will you not connect the SSR to the controller's SSR output? This output is designed to switch the SSR on and off.

Could you draw a diagram of how items are connected please?
What if I directly connected the SSR relay to the thermoregulator using terminals 11 and 12 (currently not used since the SSR is driven by the thermoregulator through the internal relay function of the thermoregulator) of the thermoregulator?

If I disconnect all the wires of the input and output of the SSR and to the input of the SSR 3+ and 4, I connect some wires that I am going to connect to terminal 11 and 12 of the thermoregulator, while in the output of the SSR I connect directly only the wires of the resistance? It might work?

I measured the direct current at the output of terminals 11 and 12 of the thermoregulator, it corresponds to 11.9 volts. Could it be fine for the relay as there is currently 22.6 volt current in use?
 

Attachments

  • [ElectriciansForums.net] SSR relay problem solution
    foto25_.jpg
    121.1 KB · Views: 40
What if I directly connected the SSR relay to the thermoregulator using terminals 11 and 12 (currently not used since the SSR is driven by the thermoregulator through the internal relay function of the thermoregulator) of the thermoregulator?

If I disconnect all the wires of the input and output of the SSR and to the input of the SSR 3+ and 4, I connect some wires that I am going to connect to terminal 11 and 12 of the thermoregulator, while in the output of the SSR I connect directly only the wires of the resistance? It might work?

I measured the direct current at the output of terminals 11 and 12 of the thermoregulator, it corresponds to 11.9 volts. Could it be fine for the relay as there is currently 22.6 volt current in use?
Yes. Ensure correct polarity, The minimum voltage is 3V and across 11 and 12 there is 12V. ssr input has to be greater than 3 and no more than 32V.
 
I have attached a picture showing you how to connect the ssr to the controller. MAke sure the SSR and controller are connected with + to + and - to -.
I solved the problem by directly connecting the thermoregulator to the SSR relay as you told me, now it works fine. Perhaps it was the rectifier bridge transformer circuit that failed, by directly connecting SSR and thermoregulator the transformer was bypassed. What do you think caused the failure? Before doing all this I also disconnected the thermoregulator from feeding the transformer through terminal 4, although the problem persisted, this shows that the thermoregulator works well. I also put some terminals on the connectors that I no longer use and I wrote the corresponding number on them, in case of a possible future use by fixing the transformer problem. The only thing is that it gets to 790 degrees in 2 hours and 20 minutes. I would need it to get to that temperature in 2 hours. If I put a fan on top of the SSR would I be able to reduce the time? When the oven was open and reached 500 degrees, the relay by touching it above had a temperature slightly above that of the environment. Then I had to close the panel and turn the oven to test it up to 790 degrees.
 

Attachments

  • [ElectriciansForums.net] SSR relay problem solution
    photo_2022-07-04_20-50-37.jpg
    96.7 KB · Views: 27
  • [ElectriciansForums.net] SSR relay problem solution
    photo_2022-07-04_20-50-37 (2).jpg
    129.8 KB · Views: 22
Installing a fan will not help. Why do you have to reach 800C in 2 hours? What difference does 20 minutes more have?
For a matter of saving time in the long cooking process of the flasks and the goldsmith casting. There are heat losses from the opening door and the hole where the oven exhaust pipe is, perhaps trying to contain them using ceramic fiber or other heat resistant materials I could reduce the time.
 
For a matter of saving time in the long cooking process of the flasks and the goldsmith casting. There are heat losses from the opening door and the hole where the oven exhaust pipe is, perhaps trying to contain them using ceramic fiber or other heat resistant materials I could reduce the time.
Please don't ignore the PID tuning advice.
You need to find out if the longer heating time is due to the controller "slowing down" the heating as set temp approaches.
or it may be that it's just the time it takes because of the thermal mass of the oven and the power of the heating element.

The controller has to be set to balance power "= speed of heating" vs overshoot. If you don't want to exceed 800 deg, it will take longer to heat the oven than if it doesn't matter about overshoot. See illustration below. Have you looked into these settings?
There's plenty on the web about this if you haven't investigated it already.
[ElectriciansForums.net] SSR relay problem solution
 

Here is a youtube clip which explains how to set up the controller initially and then to select auto tune (AT) to optimise how the oven heats up and then regulates its temperature. It is the same controller as the one you have although it has a different name.

Here is leaflet on your controller but I recommend you use the YouTube clip first.

https://images-na.ssl-images-amazon.com/images/I/91cH5fgtECL.pdf
 
Also, remember it could take 2 to 3 hours to tune if your set point is really high.
 

Reply to SSR relay problem solution in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
689
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
657

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top