Had an EV charger installed in July last year. It’s wired directly off the mains.

Since end of November anytime I plug the car in to charge, the earth/ground wire in the cabling in other appliances in the house is overheating and melting components of the appliance until the main RCD trips.

Has anyone ever seen or heard this happening before and what could be happening?
Even appliances isolated by switch fuses, when off are getting impacted. It’s concerning.

Electrician has been doing tests but is not quite sure what could be causing the fault
 
New fuse and meter supplied and readings they’re getting all good.
Their only comment was on the earth cable going from our unit into theirs, that it was too small but not major. Something to fix whenever electrician is out again
 

Attachments

  • [ElectriciansForums.net] EV charger causing ground overheating
    7C81C2A8-423C-4852-804F-593E0246C64A.jpeg
    206.6 KB · Views: 93
Good stuff. So that leaves the question of whether any of your wiring was damaged by the diverted neutral current. What were the original symptoms exactly?
 
That will be the next step yes. Initial assessment only shows damage to one particular outlet feeding one particular gas boiler appliance.
That appliance should have been earth bonded but it wasn’t. Perhaps why it was the victim or some other strange reason.
Will get that bonded, earth swapped at the meter and maybe a full survey of the inner set up. Electrician wants to rewire the board too and feed 6mm cable into the kitchen as everything bar the oven seems to be running off 1.5mm. Not sure if that’s from previous diy rewire or if it’s original cable.

The main thing is that this major issue is solved now. Takes the pressure off a little and can sleep a little better.

Any tips for what I can and can’t do to repair around where they’ve installed the new equipment?
The backer board is hideous and there’s still gaping holes around it

P.S thanks to everyone’s input on this thread. Ye saved me an absolute headache
 
Going to tag @LastManOnline in this as I'm certain he'll be interested in learning more about it.
Completely in agreement with all previous comments regarding DNO,s neutral.Its pretty certain that this house still has metallic services which are giving an excellent return path via the neighbours bonding.
 
That appliance should have been earth bonded but it wasn’t. Perhaps why it was the victim or some other strange reason.

It's a likely contender if it is connected to metallic water or gas mains that were providing the best earth path after the CNE broke open. As you say, adequate main bonding would then have prevented damage to the wiring by diverting the current along a much heavier conductor. But... would you have discovered the problem in that case, or would the pipework have been left carrying the entire house load current for the foreseeable future?

Some of us here are not huge fans of TN-C-S, even in its PME guise.
 
We also found that when we had the combi boiler installed early last year and new pipework done to meet spec, that the gas engineer never did any earth bonding on those pipes, nor did they say anything about needing to do it.
We also don't believe gas is earth bonded at the mains, despite certs from electricians, including more recently the EV install cert, claiming it is.

Strangely enough, networks called again today to upgrade the meter they installed yesterday to a new smart meter.

Recommendation again is to attach more sufficient earth cable from us to them, but also replace the black and red mains cables, the luxury for which will cost €160 for them to call out while that work is being carried out...I think that's what I read from the conversation any way. But he said the red and black were large enough for this not to be done immediately, although its near top of the list now with everything that's happened recently
 
Under the current regs, when all relevant circuits are RCD protected, the requirements and necessity of supplementary bonding e.g. around the boiler are largely eliminated. But where there are extraneous metallic service pipes, which it seems you might have, main bonding is mandatory and all the more so with TN-C-S supplies.
 
Not withstanding what was a dangerous installation regardless of the EV charger, am left wondering why the EV charger did not detect an open PEN and shut down or at least there should have been a rod for the EV charger.......... think the OP would do well to get an electrician to go through the install with a fine tooth comb
 
From the charger's point of view, it wasn't open-circuit. There was still continuity, just via the wrong conductors. There would have been extra voltage drop on account of their smaller CSA but perhaps not enough to signal an abnormal condition
 
Last edited:
Suppose it depends how it has been implemented in the EV charger. With what the OP was saying about hot earth cables around the property, i would expect to see unusual voltages and currents as measured at the EV charger, The Zappi for example has that many reference points built in to the charger that it has occasion shut down when there was no PEN issue, lol - Still think its one to note
 
New fuse and meter supplied and readings they’re getting all good.
Their only comment was on the earth cable going from our unit into theirs, that it was too small but not major. Something to fix whenever electrician is out again
The EV chargepoint shouldn't have been installed if the main protective conductor (neutralising link) was undersized. This should have been rectified first.
 
Not withstanding what was a dangerous installation regardless of the EV charger, am left wondering why the EV charger did not detect an open PEN and shut down or at least there should have been a rod for the EV charger.......... think the OP would do well to get an electrician to go through the install with a fine tooth comb
PEN fault disconnection is not a requirement of I.S. 10101.
 
Not withstanding what was a dangerous installation regardless of the EV charger, am left wondering why the EV charger did not detect an open PEN and shut down or at least there should have been a rod for the EV charger.......... think the OP would do well to get an electrician to go through the install with a fine tooth comb

There are differences between Irish and UK regs and as far as I know an earth electrode is required for the whole installation under Irish regulations when a TNCS supply is used.
 
Just had a browse on some chargers and the Tesla for example would have seen the rod and concluded no problem, assuming Earth fault detection was enabled for that install. I am pretty sure a Zappi would have gone nuts either with under-voltage L-N or N-E v Diff

Interesting though how to melt your house cables,
 
UPDATE: came home from a couple nights away to no power in the house. The main RCD had tripped.
I traced issue to blow 3A fuse in the switched fuse spur powering the gas boiler. I replaced the 3A fuse but the boiler didn't power.
Further inspection inside the boiler should me that the small fuse inside the boiler had blown.
And further inspection again showed me cabled inside the boiler had been overheating. The loom connecting all the components was melting, and the cables connecting those components to the pub had been melting too. Absolutely no idea why. Power to boiler is sound and no issues anywhere else on the circuit except for the boiler.
Gas boiler installer and repair guy is calling to replace entire boiler as opposed to just components and wiring from the last time round.
 
It sounds like a possible fault with the supply N
this may be somewhere along the supply cable or even at the substation.
a call to your energy supplier emergency hotline is the best place to start.
 
The installer should have confirmed the Ze (external earth loop) with the rest of the property off and earths disconnected. The fact that was all boxed in means this was not done

As a matter of urgency get the main gas and water pipes bondedm this way stray earth currents are likely to go through the bonding and not your boiler wiring loom

I would also suggest you contact the car charger manufacturer and ask them to send someone to asess the situation

I also noticed the EV installer appears to have installed a Hager RCD inside an Eaton unit- not good
 
Had an EV charger installed in July last year. It’s wired directly off the mains.

Since end of November anytime I plug the car in to charge, the earth/ground wire in the cabling in other appliances in the house is overheating and melting components of the appliance until the main RCD trips.

Has anyone ever seen or heard this happening before and what could be happening?
Even appliances isolated by switch fuses, when off are getting impacted. It’s concerning.

Electrician has been doing tests but is not quite sure what could be causing the fault
It's difficult to diagnose the exact cause of the fault without more information, but overheating and melting of the earth/ground wire in the cabling could indicate a short circuit or other electrical fault. The fact that other appliances in the house are also being impacted suggests that the issue may be related to the electrical system in the house rather than just the EV charger.
It's possible that the EV charger is drawing more power than the electrical system is designed to handle, causing a voltage drop and increased resistance in the wiring. This could cause the earth/ground wire to overheat and melt, and could also impact other appliances in the house.
It's important that the electrician continues to investigate the issue and performs comprehensive testing to identify the root cause of the problem. They may need to check the wiring and connections throughout the electrical system to ensure that they are properly sized and installed, and may need to perform load calculations to ensure that the system can safely handle the additional load from the EV charger.
In the meantime, it's recommended that you stop using the EV charger until the issue is resolved to avoid further damage to the electrical system and appliances in the house.
 
I also noticed the EV installer appears to have installed a Hager RCD inside an Eaton unit- not good
There is no Annex Zb derogation within I.S. EN 61439 so no conditional short-circuit rating for type tested units etc. so there is no prohibition on that. Of course this is assuming that it had been connected correctly e.g. supplied with tri-rated panel flex outer something similar.
 

Reply to EV charger causing ground overheating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

R-Fur has contacted me to post the following for him as he doesn't have access to post in the DIY section..... The DNO are required to maintain...
Replies
6
Views
4K
  • Question
Required under certain circumstances.
Replies
10
Views
3K
  • Question
they have a weird backplate where you need to remove various screws - used to be hex/security screws on some models to release it from the...
    • Like
Replies
18
Views
3K
I've done this with 2 Zappis (the customer already had one and wanted another). I upgraded the existing SWA supply cable's MCB as far as I could...
Replies
3
Views
2K
  • Question
Well lets say you are building a housing estate. Developer will arrange for DNO to lay 3-phase in the pavement on each side of the road. That is...
Replies
23
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks