Went to one of the local residents place today as she was having issues with her Zappi and Renault Zoe.
Looking at the setup it was straightforward and, whilst not necessarily the way I’d have done it, it was still compliant.
So tried to run a Zs test L-PE but got a ‘con’ error on my Megger which means the earth is either unstable or disconnected. R1-R2 was within tolerance. So I knew the continuity through was fine.
The Zoe is quite fussy and if it detects an earth problem it won’t let the car charge.
House is out in the stick and on a TT system. So I ran a Ze at the origin of the supply and this was the lowest result I got.
It was fluctuating between 688 and 746.
Someone has had the wisdom to bury the earth rod connection under some decking and flower bed. Meaning it’s inaccessible to check if it’s just loose, or poorly installed.
Ground is rocky as hell so going to be fun getting in some new rods to get the Ze below 200. May end up daisy chaining 3-4 rods just to get it down. But will see how it goes.
It has also been very dry so if the rod is not deep it probably has got that issue as well.
Might be an excuse to try one of these (and the matching SDS adaptor) to get a new rod down through rocky ground:
Already have the adapter and have quoted for the sacrificial bits.
Used them before and they are very good. I’m guessing they have only used 1 rod as I can usually get the reading somewhere around 50ohms if I use two 16mm rods.
Good to hear! I modified M16 stainless threaded rod with angle grinder to achieve much the same before.
If you can get two coupled and driven in to 2.4m depth hopefully enough damp down there for a decent reading. Beware if heavy rain soon as it could mask how dry it is capable of getting in that area.