I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican and it came out unsatisfactory which was a bit of a shock to us as we haven't done any work on electrics since new. Comments below:
Isolator (where present) is recommended for improvement. C3
Confirmation of indication that SPD is functional (651.4) is recommended for improvement. C3
For all socket-outlets of rating 32A or less, unless an exception is permitted (411.3.3) is in a potentially dangerous condition. Urgent remedial action is required. C2
For the supply of mobile equipment not exceeding 32A rating for use outdoors (411.3.3) is in a potentially dangerous condition. Urgent remedial action is required. C2
For cables concealed in walls at a depth of less than 50mm (522.6.202; 522.6.203) is in a potentially dangerous condition. Urgent remedial action is required.C2
For cables concealed in walls/partitions containing metal parts regardless of depth (522.6.203) is in a potentially dangerous condition. Urgent remedial action is required. C2
Additional Comments:
The electrical installation does not comply with BS7671, metal consumer unit partial rcd, no afdd, no spd
I have attached picture of the main consumer unit which is what the electrican was referring to. He said due to Glenfell Tower, these regulations apply from 2020 and consumer unit needs to be upgraded. Cost of replacement including VAT, Labour and materials: Ā£550. Is the electrican correct? Also the charges seem high but I'm not sure what these go for.
I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican and it came out unsatisfactory which was a bit of a shock to us as we haven't done any work on electrics since new. Comments below:
Isolator (where present) is recommended for improvement. C3
Confirmation of indication that SPD is functional (651.4) is recommended for improvement. C3
For all socket-outlets of rating 32A or less, unless an exception is permitted (411.3.3) is in a potentially dangerous condition. Urgent remedial action is required. C2
For the supply of mobile equipment not exceeding 32A rating for use outdoors (411.3.3) is in a potentially dangerous condition. Urgent remedial action is required. C2
For cables concealed in walls at a depth of less than 50mm (522.6.202; 522.6.203) is in a potentially dangerous condition. Urgent remedial action is required.C2
For cables concealed in walls/partitions containing metal parts regardless of depth (522.6.203) is in a potentially dangerous condition. Urgent remedial action is required. C2
Additional Comments:
The electrical installation does not comply with BS7671, metal consumer unit partial rcd, no afdd, no spd
I have attached picture of the main consumer unit which is what the electrican was referring to. He said due to Glenfell Tower, these regulations apply from 2020 and consumer unit needs to be upgraded. Cost of replacement including VAT, Labour and materials: Ā£550. Is the electrican correct? Also the charges seem high but I'm not sure what these go for.