Discuss EICR Unsatisfactory - New Property in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Because they want to charge you for a full board change and/or are incompetent.Thanks for the reply. But would fitting 4 x RCBO's resolve the C2's that were highlighted in my EICR? Assuming there are RCBO's out there for my unit. I know some have said it is available on here and have been recommended here which differs to what electricans here have told me that it won't work in plastic units.
What's given you this idea? Anyone can look inside their unit as long as they follow some basic safety principles like don't touch anything inside.How would I fit the model number without opening up the whole unit which is screwed in which only a qualified electrican can do?
You don't need to open it up. Starbreaker RCBOs are the only ones that fit, you need the compact version as the taller ones are difficult to fit.
Blimey, please don't open up your consumer unit @AjayS2367Because they want to charge you for a full board change and/or are incompetent.
What's given you this idea? Anyone can look inside their unit as long as they follow some basic safety principles like don't touch anything inside.
It's pretty (very) odd that 3 electricians have said this, I.e exactly the same thing. I do think it's good to keep an open mind. There is the chance that the OP is missing out some other information, so we're missing the bigger picture.
I know that's sounding a bit airy fairy, but it just seems so odd that 3 electricians have said the same thing.
I'm not telling them to open it, just commenting on the idea that somehow you need to be qualified to take the lid off your unit.Blimey, please don't open up your consumer unit @AjayS2367
It's pretty (very) odd that 3 electricians have said this, I.e exactly the same thing. I do think it's good to keep an open mind. There is the chance that the OP is missing out some other information, so we're missing the bigger picture.
I know that's sounding a bit airy fairy, but it just seems so odd that 3 electricians have said the same thing.
The EICR you posted shows a set of test results, which implies the relevant circuits have already been tested. However there are some discrepancies in the test sheets compared to what is actually installed, so I would be reluctant to believe the previous results. It is not unknown for them to be made up.They definately advised me the information as mentioned here. I know it sounds odd but I wouldn't of posted here otherwise. I have spoken to another sparks and he advised it could be done but the circuits need to be tested first as MCBs could trip RCBOs and so circuits definately have to be tested first and then advising if it can be done. I am currently looking into this once he quote for testing.
Sounds reasonable and is what I would do. I wouldn't fit based on someone else's results and would insist I test it myself.They definately advised me the information as mentioned here. I know it sounds odd but I wouldn't of posted here otherwise. I have spoken to another sparks and he advised it could be done but the circuits need to be tested first as MCBs could trip RCBOs and so circuits definately have to be tested first and then advising if it can be done. I am currently looking into this once he quote for testing.
You don't have to be qualified to do that, but you dont have to do that to find out compatibility. Just the name of the breakers that fit the current board will suffice, any good wholesaler will know.Regarding opening the MCU, I have opened the outer transparent lid many times but it has no model number specified, I was referring to removing the two screws that hold the front face of the box and whether the model or serial no is inside.