[ElectriciansForums.net] Can anyone tell me what is wrong/incorrect.
 
Morcombe and Wise, Two Ronnies???

Might I direct you fine gentlemen to another thread….

 
Glanding the cable to a metal fused-switch like the Wylex ones would have been far better, then double insulated tails to the meter.

It looks like the "filler" insulation around the 3 cores has been clamped or similar - wonder how that dent happened?View attachment 112405
Didn’t even see that dent/damage.
Looking at the size of the damage, it could have possibly been some sought of over tightened Earth strap? (But why)? I’ve run out of idea.

Merry Xmas
 
The earth tag does not match the template laid out in BS7671.

The text should read,

"Safety Electrical Connection, Do Not Remove"

Not,

"Safety Electrical Earth, Do Not Remove"

I'd also argue the Hepworth branding should not be there and the standard Earth pictogram is not used.

Pedantic, yes, but it is a noncompliance.
 
mmm! not so sure Id agree it as a non-compliance, Isn't there a passage in the regs that says "alternative 'systems/methods' etc shall not be precluded as long as safety isn't impaired" (or something like that as I Don't have regs book to hand )?

Alternative wording/pictograms hardly impairs safety and message is clear enough!
 
mmm! not so sure Id agree it as a non-compliance, Isn't there a passage in the regs that says "alternative 'systems/methods' etc shall not be precluded as long as safety isn't impaired" (or something like that as I Don't have regs book to hand )?

Alternative wording/pictograms hardly impairs safety and message is clear enough!
OK so I was clutching at straws but it is the kind of thing examiners include solely to stop people getting full marks.
 
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.

The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.

With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….

[ElectriciansForums.net] Can anyone tell me what is wrong/incorrect.
 
Last edited:
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.

The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.

With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….

View attachment 112486
They replaced meter tails with SWA making the MET remote.
We don't know how the swa terminates or if it is downstream fused.
A bit of a botch, whatever way you look at it.

A Spn fused connection unit would have been the way, but even then could cause a moan from the dno for using the meter cabinet.
 
Last edited:
I'm not sure the polarity is wrong, but probably the tails are incorrectly identified.

Many meters have L-N-N-L terminal lay-out.

Whichever though, its not correct.
You are correct, Marconi got his crayons mixed up😁
 
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.

The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.

With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….

View attachment 112486
I'd suggest the opposite.
Suppose you lose the connection between MET and CU ? Your bonding is now probably via the 0.75mm flex to the boiler. By running a connection direct from service head to CU and also taking your bonding cables to the CU, you've eliminated two connections and reduced the risk of incomplete/ineffective bonding.
 
I do like these meters with the integrated isolator built in

I actually suggested (to SELECT) about 16 years ago when they were involved in the consultation for smart meters that these new meters should have a built in isolator

The feedback- it was refused as it would cost an extra £6 per meter.
 
The feedback- it was refused as it would cost an extra £6 per meter.
This is why experienced engineers should be making the regulations not brain dead office staff. Surely a separate isolator in an enclosure and the extra time required to fit it would add up to more than £6?!
 

Reply to Can anyone tell me what is wrong/incorrect. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
i think dan was referring to the OP where they mentioned it was found when removing mirrored wardrobes.... maybe nothing to do with the mirror...
Replies
9
Views
752
  • Question
Probably for an old TV amp as little spark said
Replies
4
Views
421
  • Question
Sorry for the late reply I found it very difficult to find work but I’m not sure if this was down to Covid and all the lock downs happening just...
Replies
2
Views
489
R
  • Article
Can anyone help me identify these bathroom taps please? Hi Can anyone identify the make and model of these taps please? We have one dripping...
Replies
0
Views
176
Richt5a
R
  • Question
Thanks James, that's very helpful, give s me loads to get sorted now, fingers crossed for a safe outcome.
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks