The earth tag does not match the template laid out in BS7671.
The text should read,
"Safety Electrical Connection, Do Not Remove"
Not,
"Safety Electrical Earth, Do Not Remove"
I'd also argue the Hepworth branding should not be there and the standard Earth pictogram is not used.
Pedantic, yes, but it is a noncompliance.
mmm! not so sure Id agree it as a non-compliance, Isn't there a passage in the regs that says "alternative 'systems/methods' etc shall not be precluded as long as safety isn't impaired" (or something like that as I Don't have regs book to hand )?
Alternative wording/pictograms hardly impairs safety and message is clear enough!
OK so I was clutching at straws but it is the kind of thing examiners include solely to stop people getting full marks.
I am no expert on the regulations but wondered whether the sixth item is that the main equipotential bonding is done remote from the cutout location.
The according to the book ‘rule abiding‘ installation should have the earth conductor from the incoming N in the cutout going only a short distance to the main earth terminal bar, and then from this bar runs a cpc conductor to the dist boards, and separate EP bonding conductors for say water and gas connected also to the bar as in this figure.
With this scheme the cpc wiring and EP wiring do not share one conductor which might be considered a possible single point of failure. Just musing….
They replaced meter tails with SWA making the MET remote.
We don't know how the swa terminates or if it is downstream fused.
A bit of a botch, whatever way you look at it.
A Spn fused connection unit would have been the way, but even then could cause a moan from the dno for using the meter cabinet.
I'd suggest the opposite.
Suppose you lose the connection between MET and CU ? Your bonding is now probably via the 0.75mm flex to the boiler. By running a connection direct from service head to CU and also taking your bonding cables to the CU, you've eliminated two connections and reduced the risk of incomplete/ineffective bonding.
London UK
Other
If other, please explain
Electrical Assessor
Can anyone tell me what is wrong/incorrect.
UK
Penguin,
Simon47,
