selectivity 60898 b6 to same | on ElectriciansForums

Discuss selectivity 60898 b6 to same in the UK Electrical Forum area at ElectriciansForums.net

newfutile

-
Nearly Esteemed
Arms
Supporter
Joined
Aug 30, 2011
Messages
528
Reaction score
418
Location
hemel hempstead
I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store .
clearly we have no selectivity here ,would changing the feed mcb to a type C possibly 10 amp help achieve this?
its only on 1.5 swa so I can’t go too high ,my ZDB is 1.05 ohms
 
Last edited:
You need to look at pages 416 and 417 of regs book, and also see if the MCB manufacturer publishes a selectivity chart (assuming they are both same brand).
 
the time current curves don’t appear to say , also I guess they will only be selective for over currents , at a fault current of 228 amps there cant be any selectivity Eaton seem to suggest?
[ElectriciansForums.net] selectivity 60898 b6 to same
 
the time current curves don’t appear to say , also I guess they will only be selective for over currents , at a fault current of 228 amps there cant be any selectivity Eaton seem to suggest?

As a general rule of thumb for MCBs within the standard range of 6A - 63A they don't achieve selectivity on fault currents.

This is why MCBs are generally unsuitable for protecting distribution circuits.

BS88 fuses on the other hand have a selectivity ratio of 1.6 so if an upstream fuse is rated at least 1.6x the rating of the downstream device you will get selectivity.
 
As suggested above, you don't need the 2nd MCB here. A switch would do if some local means of isolation is needed.

However, is it a problem? True under fault conditions it is pretty much sure both will trip, but if that likely to present danger or unacceptable trouble for the owner?

If the supply was from another locked location I can see why it would matter, but if it is just two locations within one property, and nothing else is dependant on the upstream MCB remaining closed, then not worth worrying about.
 
I have changed the supply to a 16 amp mcb , my ZS at the bin store light is 1.29 ohms ,fault current of 186 amps.
my read of the time current curves is that the local 6 amp will trip possibly the 16 amp as well ,so I may not have achieved much at all!
[ElectriciansForums.net] selectivity 60898 b6 to same
 

Reply to selectivity 60898 b6 to same in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
The norm is that it goes from the DSO (ESB) fuse to a DSO isolator with a contractor's side, and then to the main overcurrent device. The ESB...
Replies
9
Views
3K
  • Question
Think all electricians will/have received a belt in their time. Doesn't matter how many time you read something like this, and are told to L-N N-E...
    • Like
    • Informative
    • Thanks
Replies
15
Views
3K
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
1K
It's fine, if you are launching with a TP MCB; that makes it one 3-phase 4-wire distribution circuit which only needs one neutral. It might be the...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks