After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch | Page 2 | on ElectriciansForums

Discuss After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

Joined
Aug 6, 2022
Messages
14
Reaction score
8
Location
London
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection.

Was after a larger unit with full RCBOs. Every Sparky I've spoken to has varied in their suggested plans.

1) Some say do an EICR first, others happy to just go straight with a new CU. EICR seems to add a big upfront cost.
2) Some mention DP RCBO, others don't.
3) One said for Building control notification, I've have to check the date on your smoke/heat & carbon monoxide alarm (?).
4) One said gas/water pipe bonding would be required and it's extra
5) One said, I'd have to get an isolator switch fitted by my supplier before the CU can be replaced. Currently there is only a mains fuse for isolation. The CU and mains fuse are both next to each other.

Prices vary for 1, 2, 3 significantly, I mean the most expensive quote is literally double the cheapest quote!

Any advice would be appreciated as this is driving me nuts!
 
A dual CU with a pair of rcds and sp rcbos would be compliant.

The use of Dp rcbos is still not a requirement, you can't call it a requirement or say it's needed if there are other ways of doing things.

There's a strong argument against this position from the perspective of potential nusiance tripping. It's one of those areas I'd raised where regs can be considered open to interpretation. I'd be happy to defend my position and I'm sure you'd be happy to do the same. Where our positions differ is that you'd likely be happy to install DP RCBOs at the insistance of a client, whereas I might refuse to install a dual RCD board if I felt there was good reason to do so.
 
There's a strong argument against this position from the perspective of potential nusiance tripping. It's one of those areas I'd raised where regs can be considered open to interpretation. I'd be happy to defend my position and I'm sure you'd be happy to do the same. Where our positions differ is that you'd likely be happy to install DP RCBOs at the insistance of a client, whereas I might refuse to install a dual RCD board if I felt there was good reason to do so.

I haven't fitted a dual rcd board for many years and am not likely to do so :)

I always fit dp rcbos :)
But I'm not required to do so :)
 
I haven't fitted a dual rcd board for many years and am not likely to do so :)

I always fit dp rcbos :)
But I'm not required to do so :)

You're not required to do so in the circumstances in which you fit them or you believe there's no circumstance in which they need to be fitted?


My limited experience has already involved a couple of faults in which N-E issues caused subsequent problems on other circuits. I like the idea of knowing a future problem should be isolated with the circuit on which it occurred, thus further avoiding the possibility of nuisance tripping.

Most customers have the means to cover an additional few % on the overall job cost and also have the ability to understand a basic explanation for those costs. Customers who have to shave every penny from a job often aren't going to like my proposals anyway (and I'll seek to avoid them) and for customers who are of limited means I'll obviously aim to find a sensible accomodation that involves keeping costs low, while incorporating as much future convenience as possible.

No customer is ever going to thank me for the power not going off on more circuits than necessary, but I'm content knowing my ears won't burn too much if only one circuit goes off.
 
As this is in danger of going round in circles I will finish up. The usual and preferred arrangement with a small tt installation is a 100ma or above S type rcd main switch and rcbo's. With this arrangement dp rcbo's are effectively a requirement IMO . Other arrangements may be devised,as above,in which dp rcbo's would not be a requirement. ( A dual rcd board AND rcbo's..🥺.).Remember....main bonding is a requirement....except when it isnt.
 
As this is in danger of going round in circles I will finish up. The usual and preferred arrangement with a small tt installation is a 100ma or above S type rcd main switch and rcbo's. With this arrangement dp rcbo's are effectively a requirement IMO . Other arrangements may be devised,as above,in which dp rcbo's would not be a requirement. ( A dual rcd board AND rcbo's..🥺.).Remember....main bonding is a requirement....except when it isnt.
Why would you have an rcd main switch with a full dp rcbo board ?
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
If the db isn’t remote from the cut out and tails are properly installed a main switch with dp rcbos is compliant adding an upfront rcd is going to reduce selectivity
 
If the db isn’t remote from the cut out and tails are properly installed a main switch with dp rcbos is compliant adding an upfront rcd is going to reduce selectivity
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
 
Not a main switch in a db, I use a separate RCD main switch which provides back up fault protection in case of rcbo failure, and protects the metal frame of the db rather than relying solely on mechanical protection to the tails.
If the db isn’t remote from the cut out and are properly installed a main switch and dp rcbos is compliant
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
sp rcbos on a tt with a main switch would have no selectivity with a N to E fault.

I think the issue is making a statement saying Required or Needed means that there are no other options.
 
Last edited:
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
You just said it again “ dp rcbos are required”.

Dp rcbos are not a requirement they are an option.
 
I think you are rather mis-interpreting. I have only ever stated that where an upstream s type rcd is used in front of a db with rcbo's single pole rcbo's would not be compliant and therefore by default are required in that situation.I stand by that.
 
I think you are rather mis-interpreting. I have only ever stated that where an upstream s type rcd is used in front of a db with rcbo's single pole rcbo's would not be compliant and therefore by default are required in that situation.I stand by that.
Look at the definition of Required.

Your post @ 34 says sp rcbo with main switch would be compliant?
 
A main switch....not an rcd main switch. A db with a main switch and sp rcbo's would be compliant. It is not the way i would do it though.
Add a s type rcd main switch and the sp rcbo's are no longer compliant.
 
A main switch....not an rcd main switch. A db with a main switch and sp rcbo's would be compliant. It is not the way i would do it though.
Add a s type rcd main switch and the sp rcbo's are no longer compliant.
I wouldn’t add an upfront rcd at all

Dp rcbos with main switch would be much better although not a requirement 🙄
The use of an upfront rcd should be avoided if possible.
 
Last edited:
And - just to throw a spanner in the works!

Regulation 411.5.2 (Just refreshing memory on TT systems) states;
One of the following i) RCD OR ii) Overcurrent Protective Device shall be used, with;

Note 1 "An appropriate overcurrent protective device device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured."

Now we know in the real world a 'permanently and reliably low value of Zs' is unlikely, but hyperthetically, installing a RCD is not necessarily a god given!
 
And - just to throw a spanner in the works!

Regulation 411.5.2 (Just refreshing memory on TT systems) states;
One of the following i) RCD OR ii) Overcurrent Protective Device shall be used, with;

Note 1 "An appropriate overcurrent protective device device may be used for fault protection provided a suitably low value of Zs is permanently and reliably assured."

Now we know in the real world a 'permanently and reliably low value of Zs' is unlikely, but hyperthetically, installing a RCD is not necessarily a god given!
Irrelevant.
All I have stated is that where an up front rcd is used sp rcbo's would not be compliant. I have not suggested any of the above is required, only the requirements where they are used.
 
In that instance sp rcbo's would be compliant. I have never said otherwise, and I have always stated an s type rcd main switch which will give selectivity. But many, myself included prefer to have the added insurance of an up front(s type) rcd on a tt, and in that case dp rcbo's are required. I have never stated that is the only option.
If something is REQUIRED then that would mean that you MUST use DP rcbos when using an up front rcd, but that's not the case as there are other options to having to use dp rcbos.

Meaning that it's not a requirement.
 
[ElectriciansForums.net] After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch
 
If something is REQUIRED then that would mean that you MUST use DP rcbos when using an up front rcd, but that's not the case as there are other options to having to use dp rcbos.

Meaning that it's not a requirement.
I have never stated dp rcbo's MUST be used where an upfront rcd is in service, if you read back through my posts I clearly agree other options are compliant such as a dual rcd board.
What I do state (very clearly I believe) and stand by is that wherre rcbo's ARE used......they must be dp where there is a upstream s type rcd and in that arrangement are effectively a requirement, you seem incapable of understanding that I am only refering to where rcbo's ARE used. I believe i have been quite clear that with other arrangements sp rcbo's are compliant.
Perhaps you would be good enough Mainline to answer this.

Lets say you have a job where the designer has specified DB's with rcbo protection to all final circuits. A main switch of s type rcd is also specified. Its a TT earthing system.
Would you install sp rcbo's and provide an EIC on completion?
 

Reply to After a New Consumer Unit, now I need EICR & 100A DP Isolation Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
1K
  • Question
Our house in a row was built in 1971 and we have metric cables with cpcs for the lighting, top of the row imperial and no cpcs.
Replies
8
Views
1K
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
3K
  • Question
Could someone kindly share why the SPD unit must be in parallel? I'm confused sorry! Hard to say without a basic wiring diagram of the current...
Replies
21
Views
6K
I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
291

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks