Hi I'm currently doing C&G 2365 Level 3
I'm working through the 305 design assignment (Swimming pool, hotel etc.)
Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few
Q2 d. Show how each circuit in the new hotel extension is to be arranged.
Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.
Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.
I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.
And finally filling out the table Q4
Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?
I can upload pictures if need be.
Thankyou very much!
Sam
I'm working through the 305 design assignment (Swimming pool, hotel etc.)
Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few
Q2 d. Show how each circuit in the new hotel extension is to be arranged.
Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.
Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.
I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.
And finally filling out the table Q4
Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?
I can upload pictures if need be.
Thankyou very much!
Sam