Hi I'm currently doing C&G 2365 Level 3
I'm working through the 305 design assignment (Swimming pool, hotel etc.)

Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few

Q2 d. Show how each circuit in the new hotel extension is to be arranged.

Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.

Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.

I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.

And finally filling out the table Q4

Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?

I can upload pictures if need be.

Thankyou very much!
Sam
 
Hi Sam,

Also in the process of doing this.

You have to show calculations for all the circuits within the table. Took me a very long time, still actually completing the calculations.

The drawings sounds like you’ve done them right, just remember with the pool/cafe to keep circuits under 30m. I had to add either more boards or split the circuits to stay in this. The specifications does give you all the details you need. Don’t forget the drops to the switches.

61009-1 for every circuit is fine as well. You have to use manufacturers data to provide reasoning why you’re using it and if it meets the Pfc. I’m just about to do this so will happily update you once it’s marked.

For the calculations, I’ll check what I’ve done and update you as I’ve had it marked and okayed for the circuits I’ve done so far.

About to take in question 6 diversity so need advice on that as well.

All the best and will update you on calcs asap

Andew
 
Upvote 0
Hi Sam,

Also in the process of doing this.

You have to show calculations for all the circuits within the table. Took me a very long time, still actually completing the calculations.

The drawings sounds like you’ve done them right, just remember with the pool/cafe to keep circuits under 30m. I had to add either more boards or split the circuits to stay in this. The specifications does give you all the details you need. Don’t forget the drops to the switches.

61009-1 for every circuit is fine as well. You have to use manufacturers data to provide reasoning why you’re using it and if it meets the Pfc. I’m just about to do this so will happily update you once it’s marked.

For the calculations, I’ll check what I’ve done and update you as I’ve had it marked and okayed for the circuits I’ve done so far.

About to take in question 6 diversity so need advice on that as well.

All the best and will update you on calcs asap

Andew
Thanks for the reply mate! Been a bit busy lately so haven't got much more done. I missed the 30m limit at first but was only lighting that exceeded so easily changed. I've done most of the calculations now just need to do the basement area. I'm guessing I'll have to do calcs for my distribution circuit down there to determine the Zs and Pfc of the final circuits.
Did you have to apply the factor for conductor resistance at maximum operating temperature? Wo calculate r1+r2. I applied the factor for ambient temperature and then again for maximum operating temperature but think I should have left out the ambient temp factor...
I can send you my calcs and see how they compare?

Thanks
 
Upvote 0
Hi both, I am currently doing the same project! did a post last week but no reply sadly. i would be grey grateful if you could help provide some guidance as i am struggling on some questions. i am also a bit worried that the drawings need to be done to scale which i havnt done. any help at all will be amazing. this is for the hotel extension project 😃
 
Upvote 0
Hi I'm currently doing C&G 2365 Level 3
I'm working through the 305 design assignment (Swimming pool, hotel etc.)

Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few

Q2 d. Show how each circuit in the new hotel extension is to be arranged.

Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.

Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.

I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.

And finally filling out the table Q4

Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?

I can upload pictures if need be.

Thankyou very much!
Sam

Hi I'm currently doing C&G 2365 Level 3
I'm working through the 305 design assignment (Swimming pool, hotel etc.)

Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few

Q2 d. Show how each circuit in the new hotel extension is to be arranged.

Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.

Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.

I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.

And finally filling out the table Q4

Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?

I can upload pictures if need be.

Thankyou very much!
Sam
Hi Sam,
I am also doing the same project on design assignment unit 305 2365 level 3. if you could help me with this projects? i am bit confused regarding circuit summary and names and what shall i add to the list. thank you for you help in advance and really appreiated.
 

Attachments

  • [ElectriciansForums.net] 305 Design Assignment guidance needed
    design.jpeg
    159.4 KB · Views: 62
Upvote 0
Hi I'm currently doing C&G 2365 Level 3
I'm working through the 305 design assignment (Swimming pool, hotel etc.)

Other then this assignment I have 1 exam for inspection and testing and a few practical days before completing.
I have done a fair few searches on google about this project a lot of the time bringing me to this forum.
I just wanted to check I'm doing these questions correctly. I feel confident with most except a few

Q2 d. Show how each circuit in the new hotel extension is to be arranged.

Is this asking to draw the circuits? I have done it this way. So from a submain in the hallway cupboard, distribution circuits to db's in each room (in purple). Then from the submains inside rooms, 1 circuit from the db to each socket outlet and fcu (in green). 1 circuit from db to air handling unit (fused spur) in red.

Then Q3 select with the aid of manufacturers data, suitable protective devises for this contract.

I was going to use 61009-1s for all final circuits, 60898s or 88s for distribution circuits supposing they dont require rcd protection, I assume surface run etc. Also 60898 for fire alarm circuit.

And finally filling out the table Q4

Ib is P/V
In should be equal to or greater then Ib
It is tabulated current worked out from In/Ca x Cg etc.
Iz is the curent carrying capacity of the chosen cable + method of installation?

I can upload pictures if need be.

Thankyou very much!
Sam
Hi, I was wondering if you could help me with project. I am also working on this. That would be a charming Favour from your side.
 
Upvote 0
Hi Sam,

Also in the process of doing this.

You have to show calculations for all the circuits within the table. Took me a very long time, still actually completing the calculations.

The drawings sounds like you’ve done them right, just remember with the pool/cafe to keep circuits under 30m. I had to add either more boards or split the circuits to stay in this. The specifications does give you all the details you need. Don’t forget the drops to the switches.

61009-1 for every circuit is fine as well. You have to use manufacturers data to provide reasoning why you’re using it and if it meets the Pfc. I’m just about to do this so will happily update you once it’s marked.

For the calculations, I’ll check what I’ve done and update you as I’ve had it marked and okayed for the circuits I’ve done so far.

About to take in question 6 diversity so need advice on that as well.

All the best and will update you on calcs asap

Andew
Hi, If you had completed this project, can u provide a detailed explanation of that or just share the completed project. That could also helped me with that.
 
Upvote 0
Hi, If you had completed this project, can u provide a detailed explanation of that or just share the completed project. That could also helped me with that.
Why would anyone share their hard work?
Have you started your project?
 
Upvote 0
Why would anyone share their hard work?
Have you started your project?
yes just started on the project. If someone can share their work, it will be helpful for those who want to do. My project is similar to those so if anyone can share, I might get my project done. The key concepts and ways to solve the problem would definitely help someone to do their own project.
 
Upvote 0
yes just started on the project. If someone can share their work, it will be helpful for those who want to do. My project is similar to those so if anyone can share, I might get my project done. The key concepts and ways to solve the problem would definitely help someone to do their own project.
Summary: If someone can send over to me all their work I will be able to complete my assignment. Thank you. Word it how you like I would be embarrassed to post such and would rather be up day and night working then go that route.
 
Upvote 0
yes just started on the project. If someone can share their work, it will be helpful for those who want to do. My project is similar to those so if anyone can share, I might get my project done. The key concepts and ways to solve the problem would definitely help someone to do their own project.
Feel free to ask questions on here but someone handing you a completed project is not the way forward. I assume you are fairly conversant with circuit design?
 
Upvote 0
yes just started on the project. If someone can share their work, it will be helpful for those who want to do. My project is similar to those so if anyone can share, I might get my project done. The key concepts and ways to solve the problem would definitely help someone to do their own project.
Your profile states to are a qualified electrical engineer?
 
Upvote 0
Sure, I would follow the rules and guidelines for it.
Well that is good to hear and a lesson for all to adopt.
But...
Just to confirm my understanding (old and not always with it), my understanding being that now as it once was, the rules and guidelines require the project to be all your own work and not the work copied from some other person and handed in as if it was yours (?)

After all why would anyone want to do anything else? More so when the intention is to one day work in a career with a legal requirement for competency. Where the safety of life and property is at risk from those who present a false record of achievement.

Anyway good for you for following the rules and guidelines
 
Last edited:
Upvote 0

Reply to 305 Design Assignment guidance needed in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
464
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
952
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
898

Similar threads

  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
2K
  • Question
In the U.K., depending on cable type and routing, an rcd may not be required
Replies
3
Views
214

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top