Use 6181Y a wholesaler will sell cut lengths including a cpc.
I can get 1m of 3 Core HO7RNF and it is a bit tight behind the board so Id rather have one piece of cable and split it only at both ends. Thanks anyway for the advice
You will then need ferrules and a crimper.
Do I have to use crimps? Can't I just use a terminal strips included in 57A JB and wire it as on the picture below?
[ElectriciansForums.net] Extending SWA garage cable
Thanks, it worked well, but I have a problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?
Thank you. I have another problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?
Yes
Reply to Extending SWA garage cable in the UK Electrical Forum area at ElectriciansForums.net
    • Friendly
They are excellent, I have used them a few times for consumer unit relocations! They can get a bit tight with cables if you're using all the...
But why do they want a CU? That won't give them any more available power than they currently have. As it is a 2.5mm SWA cable it is presumably a...