Extending SWA garage cable
I can get 1m of 3 Core HO7RNF and it is a bit tight behind the board so Id rather have one piece of cable and split it only at both ends. Thanks anyway for the advice
You will then need ferrules and a crimper.
Do I have to use crimps? Can't I just use a terminal strips included in 57A JB and wire it as on the picture below?
Thanks, it worked well, but I have a problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?
Thank you. I have another problem. It turns out that the neutral terminal slots are too small for 10mm2 cable (it's an old CU). Can I run 6mm2 instead of 10mm2 from CU to junction box if I feed it from 30A MCB instead if 40A?
Yes
Luka,
Luka,
TrueNAS JBOD Storage Server