i have read the dti and just need some one to explain it to me abit better please.

if i install a 3.60 kw system on a single story roof do i need to earth the frame work, if so how do i earth it, do i take it back to the main pme earth or do i have to run a seperate earth to a earth rod
 
Have you been through the decision tree on page 23 of the guide. That will give you the answer. If you do not understand a particular question or do not know a particular answer then tell us what it is and we may be able to help. Not enough info yet.

Regards
Bruce
 
Are you using a transformerless inverter? If yes then earth bond array. If no then don't earth bond array.

If using a Transformerless inverter you MUST install a Class B RCD (standard split load or 30mA RCDs are NOT class B) as well as earth bond array.

If using TL inverter and the earthing arrangement to the property is TNCS then the array but be earthed via a earth electrode (earth Stake)

If the earthing arrangement is anything else other than TNCS then the earth bond cable goes back to the MET terminal.

To earth bond array attach 10mm earth cable between rails (so linking all rails together).
 
Hows This?

From the DTI guide
 

Attachments

  • [ElectriciansForums.net] info on earthing the pv frame
    Earthing Snip.JPG
    49.7 KB · Views: 170
Im still really struggling with the Class B RCD thing - Some of the TL invertors have a built "Class B RCMU" "residiual current monitering unit" built to standard EN 50178 - so surly "by design" the inverter isnt able to inject DC into the AC? and therefore mitigate the need for a Class B -
 
Yes that is what the SMA documentation (posted here a few times) claims and hence their TL inverters fall into the exception case of the regulations and do not need a type B rcd
Regards
Bruce
 
Ok - i thought that was the case - i dont use SMA, but these inverters still have the RCMU built in.

Next question - if its TL - then the array will still need bonding? and if its TN-C-S it will require a spike?
 
Ok - i thought that was the case - i dont use SMA, but these inverters still have the RCMU built in.

Next question - if its TL - then the array will still need bonding? and if its TN-C-S it will require a spike?


Beware of assuming any inverter with a built in RCMU is not capable of dumping DC onto the grid in the event of a fault. This may well be the case, but unless it's certified to the relevant BS/EN thingy (I forget which one) I don't think you can fit it without a separate class B RCD. As far as I am aware, only SMA transformerless inverters meet the required standard in this respect.

And yes, if it's TL, the array will still need bonding.
 
Beware of assuming any inverter with a built in RCMU is not capable of dumping DC onto the grid in the event of a fault. This may well be the case, but unless it's certified to the relevant BS/EN thingy (I forget which one) I don't think you can fit it without a separate class B RCD. As far as I am aware, only SMA transformerless inverters meet the required standard in this respect.

And yes, if it's TL, the array will still need bonding.

Yes point taken - im confident these comply.

Regards to a spike - do you have to do a Ze on the spike? and how do you install them? just smack them into the ground were the 10mm comes down the wall?
 
Im still really struggling with the Class B RCD thing - Some of the TL invertors have a built "Class B RCMU" "residiual current monitering unit" built to standard EN 50178 - so surly "by design" the inverter isnt able to inject DC into the AC? and therefore mitigate the need for a Class B -

If you are refering to the Fronius range the RCMU does NOT meet the Class B requirements, Horses mouth from Fronius at Eco Build and again from our suppliers.
 
No im not - after reading further into it maybe they dont, its something to do with a perticuler reg VDE0100-712, were can i get a copy of that to read?

Can i ask you - If i install a seperate 2 way CU, do i need a class b 16A RCBO? or 63A class b incomer with a normal 16A mcb?
 
No im not - after reading further into it maybe they dont, its something to do with a perticuler reg VDE0100-712, were can i get a copy of that to read?

Can i ask you - If i install a seperate 2 way CU, do i need a class b 16A RCBO? or 63A class b incomer with a normal 16A mcb?

Shouldn't use RCBO's as they aren't double pole from what I have read somewhere. You will not get a Class B RCBO anyway from my investigations and a Class B RCD will be 300mA. Unless anyone knows different?
 

Reply to info on earthing the pv frame in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top