info on earthing the pv frame | Page 2 | on ElectriciansForums

Discuss info on earthing the pv frame in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Shouldn't use RCBO's as they aren't double pole from what I have read somewhere. You will not get a Class B RCBO anyway from my investigations and a Class B RCD will be 300mA. Unless anyone knows different?


OK - Just so i get this clear im my head - lets say i split the meter tails, install a small two board - were does the "class b" fit into this? If the radial upto the inverter needs 30ma RCD, how do i fit in a 300ma class b?

http://www05.abb.com/global/scot/sc...dc12576ba003c22bf/$file/solar cat lr v.06.pdf
 
Last edited:
OK - Just so i get this clear im my head - lets say i split the meter tails, install a small two board - were does the "class b" fit into this? If the radial upto the inverter needs 30ma RCD, how do i fit in a 300ma class b?

http://www05.abb.com/global/scot/sc...dc12576ba003c22bf/$file/solar cat lr v.06.pdf

Why does it need 30mA RCD protection. Is the AC embedded in a wall at less than 50mm depth? If so using SWA cable (Earthed metallic sheath) you do not need 30mA RCD protection.
The Class B can go in a module box with a MCB. Nothing stopping that. IF the inverter for any reason requires 30mA protection then a second RCD is required at 30mA (unless Fronius TL - They don't like 30mA, don't know if any issues with other makes). The Class B's only purpose is to prevent DC voltage being injected into the AC side nothing more.
Regarding the ABB link above. The F202 RCD is the correct item. The spec shows a range of 30, 300 and 500mA yet the device is 300mA.
 
ok - 300ma upstream, and 30ma downstream, its quite common to run the radial internally due to customer not wanting external cable run (dont ask it happens!), so to satisfy the big red book 30ma rcd is the easiest way to conform, and in this instance use the 300ma class b as the main switch in a seperate CU.

300ma RCD class B, 30ma RCD class A, then 16a MCB, phew what a mouthfull - shall be seeking a transformer inverter from now on.
 
ok - 300ma upstream, and 30ma downstream, its quite common to run the radial internally due to customer not wanting external cable run (dont ask it happens!), so to satisfy the big red book 30ma rcd is the easiest way to conform, and in this instance use the 300ma class b as the main switch in a seperate CU.

300ma RCD class B, 30ma RCD class A, then 16a MCB, phew what a mouthfull - shall be seeking a transformer inverter from now on.

No problem with internal cable route but is it chased in? If it is you can still use SWA saves the issues of RCD protection.

As for TL's IF SMA have it right and I don't see why they don't then the Class B is included it's just the rest of them. Until they catch up with SMA then the Class B has to be fitted. And again with any TL bonding.
 
Could you tell me where it specifies a 10mm earth and its calculation, because surely when we install large >50kw systems the earth fault current will be greater therefore the earth bond should be a larger size?
 
Could you tell me where it specifies a 10mm earth and its calculation, because surely when we install large >50kw systems the earth fault current will be greater therefore the earth bond should be a larger size?

The OP started as a domestic system where by the the likely existing bonding conductors would be 10mm. As you say the larger the electrical system the larger the bonding conductors. I see it being very unlikely a >50kW system will be installed on a domestic property.

BS7671 requires us to calculate the bonding conductor cross sectional area.
 

Reply to info on earthing the pv frame in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top