"So that I have definitely got this right could you confirm the following"
1. g83 goes up to 3.68kw after which g59 protection settings becomes the standard.
The standard G83 limit is 16A per phase (i.e. 3.68kW single phase or 11kW three-phase). For a single SSEG installation, this can be connected and then you can inform us later, providing all the commissioning documents etc to register for FIT. The standard G83 compliant inverter is acceptable (with upper frequency set to 50.5Hz). For connections >16A/phase, there has been a relaxation in the rules as given below.
2. It is possible to install up to 17kw on a single phase or 17kw per phase on a 3 phase system so long as the protection settings in the inverter are based around the g59 standard therefore negating the use of g59 relays ( this is depending on whether the line can take it )
We will accept a G83 1/1 type connection for a single SSEG installation, provided the inverters used are type-verified, and the capacity is no greater than 17kW single phase, or 50kW three-phase. You must submit an application form first (Appendix 2 of G83/1) to gain consent for connection, or to get costs for any reinforcement that maybe required. A G83 compliant inverter could be used, provided the upper frequency limit is set to 51.5Hz, or a G59/2 relay.
3. I have been quoting for a job where the customer requires approx 9.6kwp on a single phase supply. The intended design is to use 3 separate g83 inverters ,sma 3300 which as far as I am a where are configured with the g83 protection settings. Is it ok to use these inverters with the g83 settings as they individually are less than the 3.68kw limit ? The problem is I can't find a single inverter to use on a single phase which has the g59 protection settings and I don't want to get into the realm of g59 relays.
As above, the G83 protection should be set to 51..5Hz on the upper frequency