fit new 2011 sma sunny boys with limited 16amps output
G83 16A limit is based on 230V and that figure should be used in the calculation.
Parallel operation
22 (2) (a) the source of energy does not produce an electrical output exceeding 16 amperes per phase at low voltage;
Declaration of phases, frequency and voltage at supply terminals
27 (2) Unless otherwise agreed in writing between the distributor, the supplier and the consumer (and if necessary between the distributor and any other distributor likely to be affected) the frequency declared pursuant to paragraph (1) shall be 50 hertz and the voltage declared in respect of a low voltage supply shall be 230 volts between the phase and neutral conductors at the supply terminals.
a source of electrical energy rated up to and including 16 A per phase, single or multiple phase, 230/400 V ac.