R

rantoftheday

Can someone tell me why on certain installation where a main earth ain't in place ie domestic property why can't an earth be taken off main incoming neutral as a tn-c-s system instead if installing a tt system?
 
Last edited by a moderator:
If you can aprenticesprky, print out that diagram that Frank posted. It's one of the best pictorial explanations I've seen of a TN-C-S earth path in a long time.
I'll see you after me ban expires :)

This one shows the fault path.
 

Attachments

  • [ElectriciansForums.net] Neutral link to earth
    image.jpg
    140 KB · Views: 62
Sorry sintra it's self correcting text and never noticed didn't realise it was frank. Trev, ill bet your 2 yo grandson is more competent than some of my journeymen. Ps good diagram

Could be 2 for the :ban: hammer tonight :lol:

- - - Updated - - -

Sintra do you have guidance notes in electronic format?


I sure do :)
 
You can get the full package from the IET for £215.00 should work on kindle through vital source bookshelf.

IET Wiring Regulations BS 7671:2008(2011)
Guidance Note 1: Selection & Erection
Guidance Note 2: Isolation & Switching
Guidance Note 3: Inspection & Testing
Guidance Note 4: Protection Against Fire
Guidance Note 5: Protection Against Electric Shock
Guidance Note 6: Protection Against Overcurrent
Guidance Note 7: Special Locations
Guidance Note 8: Earthing & Bonding
On-Site Guide
Electrician’s Guide to the Building Regulations
Electrical Installation Design Guide: Calculations for Electricians and Designers (new edition to be added upon publication, late 2012)

Wiring Regulations Digital - Business Package - IET Electrical
 
The Magic word in PME is the M, which stands for ''Multiple'' !!

If the neutral hasn't been earthed at multiple locations along a distribution cable length, then you are just inviting trouble/disaster by making your own TNC-S link....
 
Last edited by a moderator:

Reply to Neutral link to earth in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
582
loz2754
L
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top