Hello everybody, my name is Michael.

Last week a landlord called me regarding a faulty electric shower that the company tried to re fit under warranty but told him that the cable supplying it was under rated so they couldn't finish the job...

I went to take a look and the property being a hostel type flat in London did not meet 17th edition regulations. There was no RCD present and the consumer unit was older than me (27 years). I looked at the circuit supplying the shower and it was a 6mm twin and earth on a 50amp breaker. This obviously isn't correct as the run was over 15M and the shower was 9.5KW.

Obviously a shower pulling 38amps cannot be fed via a 6mm twin and earth on a 50amp breaker unless you were after an insurance job...

So after wrestling the metal cabinet off the Crabtree fuse board I noticed it was fed via a 6mm pyro. The circuits in the board were a cooker supply, upstairs lights, downstairs lights, immersion, upstairs sockets, downstairs sockets and a shower supply... Is the 6mm pyro capable of such demand?

I couldn't gain access to the meter cupboard to see what the fuse was feeding the flat, but to me it sounds a bit under rated?

The length of run is around 30M and the cable is clipped direct...

Obviously the landlord is asking me why it needs changing if 'its worked perfectly fine all this time'. But I don't really fancy putting my name on a job if I think it's going to be on the ITV headlines the next day.

Your views are welcome.

Michael > NICEIC registered > 10 years in the business
 
I remember the first time as an apprentice making off my first pyro with the electrician watching closely. We had to make a stripping bar out of mild steel at college. having got the end started with the side cutters & then using the stripping bar (yes i did cut a foot or so off before stripping) I stripped it down to the required length & proceeded to screw on the pot by hand & then using footprints to tighten it fully,( & checking for that naughty little swarfe ring inside the pot & then blowing inside the pot to clear out the magnesium oxide powder that was when all hell let loose & made to look a complete idiot . oh well happy days.
 
As an aside copper itself tends to work harden over the years & getting the pots & seals as well as the glands for imperial sizes as used in the sixties in flats with concrete ceilings would be very difficult to get these days. If one of the conductors breaks of from the pot, whilst trying to manipulate it it becomes a real headache to deal with or if the outer sheath gets damaged the hygroscopic magnesium oxide will begin to absorb mosture & eventually will start to cause problems. Just not worth the hassell
 
You could always check this data sheet for conversion options for imperial pyro using metric seals

Don't know if they still do it but when Pyro was owned by BICC you could call the sales office and they would arrange for a pot to be drilled suit the imperial size you needed usually within 24 hours
 
You could always check this data sheet for conversion options for imperial pyro using metric seals

Don't know if they still do it but when Pyro was owned by BICC you could call the sales office and they would arrange for a pot to be drilled suit the imperial size you needed usually within 24 hours

Not heard of that for a long time now. Standard "conversion" now is a potted junction, and new cable from that to the termination. On fire anyhow, though on certain LV jobs, I've been asked to re-run the whole cable.

And yes others - the joys of pyro, or MICC - though what on earth MIMS is, is anyone's guess - Mummy's Insulated Milk System possibly?

As for the joys of wet pyro. Oh boy. Days (and nights) of fun! You very quickly learned to improvise on tools too - especially at 40 floors up from your main tool box.
 
Mineral Insulated Metal Sheath, the term is used to cover both copper and aluminium cables...

Well, now you put it like that.... I'd still far sooner work on Mummy's Insulated Milk System..... :)

Yes, it makes sense as such, I don't honestly think I've ever heard it described as such though - only as MICC or Pyro.

The aluminium is interesting - I thought we'd long done away with aluminium as a conductor for a number of reasons, and to my understanding, FP200 and similar cables which have an aluminium sheath don't qualify as MICC or MIMS...as they're not mineral insulated....

Time for me to do a little more reading up I think.
 
Well, now you put it like that.... I'd still far sooner work on Mummy's Insulated Milk System..... :)

Yes, it makes sense as such, I don't honestly think I've ever heard it described as such though - only as MICC or Pyro.

The aluminium is interesting - I thought we'd long done away with aluminium as a conductor for a number of reasons, and to my understanding, FP200 and similar cables which have an aluminium sheath don't qualify as MICC or MIMS...as they're not mineral insulated....

Time for me to do a little more reading up I think.

They made Pyro in both copper and alluminum, probably still do to some extent. I haven't seen it about for a number of years now though...

EDIT... You'll find that alluminium is still used as a conductor by the DNO's in virtually all of there distribution cables, including the bare overheads etc.... You'll also find a good deal of it in (multi-core distribution cables) being used in industry too...
 
Last edited by a moderator:
They made Pyro in both copper and alluminum, probably still do to some extent. I haven't seen it about for a number of years now though...

Never too long in the tooth to learn - in what must be thousands of miles of Pyro, I don't recall ever once coming across aluminium. Just lucky I guess :)

I do recall pulling out miles of aluminium T&E when I commenced many moons ago, however, and remember well the tables being split for copper or aluminium and having to do calcs for both at college too....
 
Well, now you put it like that.... I'd still far sooner work on Mummy's Insulated Milk System..... :)

Yes, it makes sense as such, I don't honestly think I've ever heard it described as such though - only as MICC or Pyro.

The aluminium is interesting - I thought we'd long done away with aluminium as a conductor for a number of reasons, and to my understanding, FP200 and similar cables which have an aluminium sheath don't qualify as MICC or MIMS...as they're not mineral insulated....

Time for me to do a little more reading up I think.

Pyro has been manufactured as an all copper cable, an all aluminium cable and a copper cored aluminium sheathed cable. The termination kits for the latter where labelled as ALCuMIC. Haven't done a lot with the aluminium stuff but it was not good to work with especially trying to repair it or modify an installation

I do like your alternative "Mummy's Insulated Milk System" is that when you make a boob
 
Pyro has been manufactured as an all copper cable, an all aluminium cable and a copper cored aluminium sheathed cable. The termination kits for the latter where labelled as ALCuMIC. Haven't done a lot with the aluminium stuff but it was not good to work with especially trying to repair it or modify an installation

I do like your alternative "Mummy's Insulated Milk System" is that when you make a boob

It was really with the kids in college that it came to mind lol....

I have led a sheltered life apparently, when it comes to Pyro - though I can (still) work well enough with the copper stuff we all know and love - I'm happy to confess I had little knowledge of aluminium pyro in any form. Not something on any sites at all I was on in the 80s - either for fire or power. Lucky escape, perhaps :)
 
Not heard of that for a long time now. Standard "conversion" now is a potted junction, and new cable from that to the termination. On fire anyhow, though on certain LV jobs, I've been asked to re-run the whole cable.

It's a shame BICC did away with the "shrink on" seals for Pyro made it very easy for doing repairs on imperial cable. I actually worked on a site when they were first used had the Pyro reps on site a few times sorting out the teething problems of using them on site and not in a cosy workshop
 
love Pyro, did a church in it, all bare copper, shaped around the stonework, still the job i am most proud of, its just...proper! shame that its all FP200 etc now ..

as for tools, i found that unbolting the tools off the Wrexham MICC stand in CEF's counter was a much cheaper way of getting strippers, pot crimpers etc lol.... ahhh, misguided yoof...
 
Last edited by a moderator:
It was really with the kids in college that it came to mind lol....

I have led a sheltered life apparently, when it comes to Pyro - though I can (still) work well enough with the copper stuff we all know and love - I'm happy to confess I had little knowledge of aluminium pyro in any form. Not something on any sites at all I was on in the 80s - either for fire or power. Lucky escape, perhaps :)

I started just as the Ali stuff was coming to an end in the 70's but did some repairs to installations into the 80's the all aluminium stuff was horrible as the small conductors became brittle and snapped very easily the copper cored stuff was marginally better, tightening the gland nuts had to be done carefully to avoid breaking the sheath with the olive

It's surprising how many things have come and some gone with pyro over the years there's been crimp on pot's, shrink on seals and glands that covered a number of cable sizes to name a few
 
You must be one very heavy handed electrician, is all i can say!!...lol!!

I have never broken or snapped a core off of a MICC, or the Ally stuff ever, not even the on the smallest of sizes!! Oh, and aluminium Pyro was still being used long after the 70's, i can show you miles of the stuff (all PVC sheathed) installed in mid 80's and beyond!!!

Ally Pyro, had it's own working methods and restrictictions, keep to them and there is nothing wrong with installing the cable or the cable itself.
 
Speaking of heavy handed.
An old thread, I know, but came across a couple of photos. Old 6mm 4 core MICC 3 phase oven/cooker supply in school kitchen. Called in after industrial kitchen fitters found a phase down after unit replacement.

Made an attempt to repair but insufficient length or room available. The pyro came through the floor in a 25mm conduit. Stripped a couple of inches and found the point where all 4 cores had been nicked on initial termination, causing the broken conductor after movement of the machine isolator.
You can just about make out the damage caused initially to the 2 remaining cores. A second core snapped whilst stripping. Had to give up and rewire in
swa.
[ElectriciansForums.net] 6mm pyro...[ElectriciansForums.net] 6mm pyro...
 
I miss Pyro. I hated it initially as an apprentice, but once you knew how to terminate it properly and how to make a good job of installing it the end job was far superior to any other cable method. I remember a Job we did many moons ago that was 100% pyro and I was tasked with taking all the pyro's around the switch room on tray and terminating into the various dis boards. I decided to make it a good Job to prove I could be bothered (I was only 19). I spent the best part of two weeks running them in, taking out all kinks and straightening the cables and making sure none crossed on the tray before terminating them.

I was that sad or whatever you want to call it, but I actually used brasso to clean and polish the bare pyro and some fairy to clean the PVC coated for the E-Lights, Fire alarm and exterior lights. I have never done such a job since (costs too much money to spend the time sadly).

I do have some old picture of this job when finished somewhere, I will dig them out, scan them and put them up for people to see
 
Going back to the original question, ...i was thinking, this may have not been 6mm MICC, but an imperial sized MICC cable. If so then it would of held a higher CCC than that of it's metric cousin!! Around the equivelent to 7/044 as i remember...
 
Don't know the temp rating of run of the mill terms but I remember visiting the burned out shell of a WMC in yorkshire once. Lengths of smoke blackened pyro were strung about the debris, cable and terms still intact.
 
I wonder if the Electrical Trainee sparks can fit the ceramic seals without damaging them, I know there was a lot of sparks who struggled even with the special tool supplied by, I think BICC, I spent many 12hour shifts replacing the seals.
 
I'm currently working on a decommissioning project and everything (accept a few irrelevant things like fire alarms, emergency lights...) and everything is either (heavy duty) pyro or really old (ie no outer sheath) SWA. Getting bored of ripping it out all the time, but I like seeing the over the top use of brass, huge buzz bars everywhere, cast iron controls and enamel industrial lights all over the place.

Needless to say, it would be a lot more expensive of a job to do now
 

Reply to 6mm pyro... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Ouch. Danger notice to customer in my book.
    • Like
Replies
1
Views
538
  • Question
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative
    • Like
Replies
15
Views
2K
  • Question
That's exactly what I wanted to hear.Thanks pc1966👍
    • Like
Replies
20
Views
5K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
Will do... Thank you for your help
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks