Hello everybody, my name is Michael.
Last week a landlord called me regarding a faulty electric shower that the company tried to re fit under warranty but told him that the cable supplying it was under rated so they couldn't finish the job...
I went to take a look and the property being a hostel type flat in London did not meet 17th edition regulations. There was no RCD present and the consumer unit was older than me (27 years). I looked at the circuit supplying the shower and it was a 6mm twin and earth on a 50amp breaker. This obviously isn't correct as the run was over 15M and the shower was 9.5KW.
Obviously a shower pulling 38amps cannot be fed via a 6mm twin and earth on a 50amp breaker unless you were after an insurance job...
So after wrestling the metal cabinet off the Crabtree fuse board I noticed it was fed via a 6mm pyro. The circuits in the board were a cooker supply, upstairs lights, downstairs lights, immersion, upstairs sockets, downstairs sockets and a shower supply... Is the 6mm pyro capable of such demand?
I couldn't gain access to the meter cupboard to see what the fuse was feeding the flat, but to me it sounds a bit under rated?
The length of run is around 30M and the cable is clipped direct...
Obviously the landlord is asking me why it needs changing if 'its worked perfectly fine all this time'. But I don't really fancy putting my name on a job if I think it's going to be on the ITV headlines the next day.
Your views are welcome.
Michael > NICEIC registered > 10 years in the business
Last week a landlord called me regarding a faulty electric shower that the company tried to re fit under warranty but told him that the cable supplying it was under rated so they couldn't finish the job...
I went to take a look and the property being a hostel type flat in London did not meet 17th edition regulations. There was no RCD present and the consumer unit was older than me (27 years). I looked at the circuit supplying the shower and it was a 6mm twin and earth on a 50amp breaker. This obviously isn't correct as the run was over 15M and the shower was 9.5KW.
Obviously a shower pulling 38amps cannot be fed via a 6mm twin and earth on a 50amp breaker unless you were after an insurance job...
So after wrestling the metal cabinet off the Crabtree fuse board I noticed it was fed via a 6mm pyro. The circuits in the board were a cooker supply, upstairs lights, downstairs lights, immersion, upstairs sockets, downstairs sockets and a shower supply... Is the 6mm pyro capable of such demand?
I couldn't gain access to the meter cupboard to see what the fuse was feeding the flat, but to me it sounds a bit under rated?
The length of run is around 30M and the cable is clipped direct...
Obviously the landlord is asking me why it needs changing if 'its worked perfectly fine all this time'. But I don't really fancy putting my name on a job if I think it's going to be on the ITV headlines the next day.
Your views are welcome.
Michael > NICEIC registered > 10 years in the business