My dearest Daughter bought the house she was after and I eventually got to look at her Supply arrangement.
YES that is a jubilee clip you see clamping the (undersized) earth to the sheath.. looks a bit "IFFY" but zs is .23 of an ohm..




[ElectriciansForums.net] DIY Earthing !!
 
use the adiabatic to calculate the min. size of the earthing conductor. if that comes out at, say, 4mm, then a 6mm or 10mm can't be condemned as undersized.
 
I bet you won't get much of a Ze value out of that connection!!!! That jubilee clips looks to me, as if it's been attached to the PVC sheath of that DNO cable. It certainly doesn't look like any PILC that i've ever seen in the past!!

As for your extremely poor selection of the correct cable earthing clamp to use, i think your right to leave it another electrician. Hopefully, he will know about ''Constant Force'' spring earthing clamps. Not that they would be any good, on what could well be, a concentric or split concentric cable!! lol!! Maybe better to, contact the DNO and ascertain exactly what, if any, earthing system is being supplied to this installation!!
well...
a `quick lift the lid` would make matters clearer...would it not?
 
Last edited by a moderator:
Which is exactly why I've wrote the words I have mate but just because it has a good Ze at present it doesn't make it a secure connection does it
well what we have here is duty of care & ensuring the install was good for continued service at the time of inspection & testing.....

- - - Updated - - -

its not one V the other...
 
If that was a PILC cable, the cut-out will be pitch filled, with a seal around the cable as it enters the cut-out. I can't see any form of sealing around the cable. Anyway, if that cables outer sheath isn't lead, you'll not be getting any Ze value.
 
The cable could be Jute covered PILC, but I need to see lower down the cable. There will be a point where the jute ends with copper whipping.

As for sealing a PILC without compound?
It’s easy if you have resin impregnated cotton tape. (I’m down to my last ½ roll).
There is the modern cheats method with H/S tube and a boot.
 

Reply to DIY Earthing !! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K
My girlfriend has a cousin who has lived in Japan for at least 15 years teaching English yet he can barely speak their language.
    • Like
    • Informative
Replies
4
Views
312

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top