Hi all.
As I understand it, exported earth is only an issue for PME situations? Therefore, when a domestic installation is a TT and power is to be brought out to a remote outbuilding, is there a requirement to fit a second earth electrode and if so, should this be independent of the house TT setup? I've added a crude picture of the installation scenario wiring. As you can see, if a second earth electrode is installed, I've questioned by use of the red zigzag whether there should be continuity in the earth from the house to the cabin CU, or it should be terminated without connection?

Many thanks.

[ElectriciansForums.net] Extending TT to remote outbuilding ??
 
So.......a second earth stake has to be fitted. BUT, should this be independent of the original??

A second earth rod position at the new building is the correct way to go, linking the two rod positions either with a 3rd core or the armouring of the supply SWA cable!! It is totally pointless to have 2 independant TT systems on a single installation!! Can't make it any clearer than that for you.
 
Why on earth (excuse the pun) would you not link the two earth rod positions via the 3rd core between the MET and EMT??

That was in response to the earlier post which I had quoted which was concerned with the creation of a new tt earth instead of extending what I assume was a pme earth. Not in response to the main topic here.

I thought that was clear from the post I had quoted?
 
That was in response to the earlier post which I had quoted which was concerned with the creation of a new tt earth instead of extending what I assume was a pme earth. Not in response to the main topic here.

I thought that was clear from the post I had quoted?

Ooops my post was meant as a reply to this post!! My apologies!! lol
Even then i'm not sure now, if he is talking about PME to TT?? Have to have another read through when i get home tonight!! lol!!

!!

Originally Posted by Squid_uk [ElectriciansForums.net] Extending TT to remote outbuilding ?? I recently have done a similar installation to an out building. I installed a new submain to the building with a new DB and earthing stake. I used a 16mm 3 core SWA but did not connect the 3 core (used as earth) to the house earth, therefore keeping it seperate but still protecting the submain via a 3rd core and the steel armour. Also my Ra reading was 60ohms after installing 2 stakes coupled, so as stated in earlier posts, depth is good!
 
No worries.

I assumed pme as trying to keep the new earth seperate would not be necessary otherwise. And to the best of my knowledge TNS wouldn't normally require a seperate earth system.

If I have read it right he has run a 3c swa to the outbuilding. Connected the 3rd core of the swa to the new TT earth at the outbuilding and not the earth at the supply end. Which in my opinion doesn't achieve anything.
Hopefully the armour is connected to the supply earth and isolated at the outbuilding end, otherwise the whole game is pointless. And if the armour is solely connected to the new TT earth then the Zs situation for the supply could be a bit squiffy!

Can't see the point of it all myself, a 16mm core is more than enough for a main bond for a normal house supply anyway, not to mention the armour connected in parallel!
 
Tut Tut!! Still trying to convince begineers to be lazy so and so's then!!

No...asking why you are saying in post 15 of this thread that relying on RCD's is not acceptable and yet on another thread falling over yourself to praise an Ra value of 15 ohms. You want it both ways,well you are not having it as long as I'm a member of this forum........seems to me your stance on RCD reliance is somewhat 'relaxed' where the Ra value relying on an RCD is achieved by one of the 'holier than thou clique' you are founder member of.
 
No...asking why you are saying in post 15 of this thread that relying on RCD's is not acceptable and yet on another thread falling over yourself to praise an Ra value of 15 ohms. You want it both ways,well you are not having it as long as I'm a member of this forum........seems to me your stance on RCD reliance is somewhat 'relaxed' where the Ra value relying on an RCD is achieved by one of the 'holier than thou clique' you are founder member of.

Nah, as usual you're twisting things to suit your own stance on not bothering to achieve any form of a stable working TT system!! My stance is and always has been that RCD devices (of ALL types) are not as reliable as the manufacturers would like you to believe. Unless you are able to achieve near or TN values, then an added upfront 100/300mA S type is the prudent way to go, to back up that single RCD's device that's looking after several circuits each side of the dual CU's. Nothing ''holier than thou'' about anything to do with providing a working TT system, just those that are too bloody lazy to try, ...and those that are willing to invest in making the effort!! Ridiculing those that are willing to make the effort seems to be your main objection for some god only known reason??...
 
Sorry, not having dealt much with the extending of PME, but my take is its permitted as long as the outbuilding your feeding has no extraneous conductive parts, for example building erected with steel framework sunk in ground,incoming metallic pipework e.g. Gas, Water. Etc
If the install does contain any of the above, then you need to isolate secondary earthing system from supply earthing system(pme) and Rod? Again pls don't shoot me down as I don't deal with extending PME systems.
 
Sorry, not having dealt much with the extending of PME, but my take is its permitted as long as the outbuilding your feeding has no extraneous conductive parts, for example building erected with steel framework sunk in ground,incoming metallic pipework e.g. Gas, Water. Etc
If the install does contain any of the above, then you need to isolate secondary earthing system from supply earthing system(pme) and Rod? Again pls don't shoot me down as I don't deal with extending PME systems.


NO. if there's extraneous you need to ensure that the cpc of the feed cable is adequate to act as a cpc and a bonding conductor for a PME system, or run in a separate bonding conductor. ( with domestics, this is generally 10mm ).
 

Reply to Extending TT to remote outbuilding ?? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
715
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top