Hi,

Just a general question, I have never installed an earth rod so don't have any experience in them, but would like to think I know the basics before I come across one I have to install.

My question is, presumably I would be correct in thinking the 3/8 rods are not worth the time and should be not sold, and only 5/8 should really be used, put at least two in connected vertically, depth is best I understand, should I need to install another rod to help bring the reading down, is there a recommended distance the second rod should be from the first one or would putting it a few inches away be ok?

My initial thoughts are that it would be ideal to locate it the same distance away that the first one is long, so if its a 4ft rod, put it at least 4ft from it?

And keep them a couple of meters away from the house where possible. Someone mentioned to me that putting a think 1000mm drill into the ground can help drive it in easier.

I did find a good thread on here this morning about exporting PME, or extending the equi-potential zone so to speak and needing to TT the remote end in some circumstances, it did confirm my thoughts, but made interesting reading.
 
I am in similar position UKsparks! The Ra is around 350ohms from what I can remember so I'll be putting an additional rod in. What Ra do you have? Would you really put it a couple of meters away from the house, they generally seem to be right next to it. It does make sense to keep it away from the house..How would you run the cable the couple of meters away?

Guidance note 8, section 2 is a good read although I would have no idea of the level of the water table or how to calculate the resistivity of the soil! It does give 'probable values' for soil resistivity types though which you could use to determine what length and diameter rod you need.

I'm probably getting a bit carried away though.. A thick long rod will do! :smile5:
you bet it does.

Think about it....if you put it right next to a building then alls the rod`s going to do is hit all the building rubble/foundations and whathaveyou...
 
The larger diameter the rod the better within reason, the thin rods have much less surface area and they're much more likely to bend and deviate from vertical when they're hammered in. If you need to knock in 2 or 3 or 4 rods to get a decent Ra then it's better to couple them together to make a single deep rod rather than knocking them in as separate rods.

We don't usually worry about being too close the building, by the time you've gone down 6, 8 or even 10 meters with the rod as long as you've not hit anything that stops the rod going down it makes very little difference to the Ra reading if there's builders rubble near the top. The one thing I do worry about is hitting pipes or cables so we normally dig at least the first 2-3 feet to make sure there's nothing there.
yes....caus your looking for stability...in all conditions...

a shallow rod will only be good in the wet.....the deeper you go the more you get under the soil surface....which will dry out when the sun comes out....

depth is key with TT....
 
Wow! What a great place,never thought of them going there. I imagine the readings wont fluctuate much either during the year.


Actually, ''NOT'' such a great area to place earth rods. Far better to place earth electrodes externally where rain can keep the surrounding soil wet/damp. The damper the surrounding soil, the better will be the contact between soil and electrode, and better will be the Ra values obtained.
 
The larger diameter the rod the better within reason, the thin rods have much less surface area and they're much more likely to bend and deviate from vertical when they're hammered in. If you need to knock in 2 or 3 or 4 rods to get a decent Ra then it's better to couple them together to make a single deep rod rather than knocking them in as separate rods.

We don't usually worry about being too close the building, by the time you've gone down 6, 8 or even 10 meters with the rod as long as you've not hit anything that stops the rod going down it makes very little difference to the Ra reading if there's builders rubble near the top. The one thing I do worry about is hitting pipes or cables so we normally dig at least the first 2-3 feet to make sure there's nothing there.

Unfortunately in the UK, you'd be lucky to get a single 2.2m 5/8'' rod, and very lucky indeed if you get an electrician to couple two together and get 2.4m!! Far more likely to get a non extendible 2.2m thin twig lol!!

I'll warrant that no-one here has ever driven a rod down 10 metres, or even 8 metres come to that!!
 
serious question, though. what do you do when the rod hits rock at 3 ft.?
We use a case-hardened tip that screws onto the first rod before it gets hammered in, 8 times out of 10 it will go through loose rock when used in conjunction with a jack hammer with an SDS Max rod driving attachment.
[ElectriciansForums.net] Earth rod spacing
 

Reply to Earth rod spacing in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top