Just been to look at a job subing to grain drying firm to help then installing cables, lighting etc. The mains is 3ph in house, across newly tarmac to a small out house were it goes to db, then off to variouse sub dbs. The main swa from house is 16mm 4 core, swa as earth. ( No 300 / 500ma main switch in house.) From here it will run to the main board to the new grain shed. There electrican says put 300ma main switch on db in grain store and make it to tt, (as they havent priced to altet anything) But I thought it should be a source. So I proposed making main swa in to tt system / eart rod / 300 ma, then all of farm protected and wont trip the current farm house. Ah this is a arable farm, no livestock ever present, am I right or totally wrong and should keep my thoughts to my self
 
What is the original earthing arrangement anyway? You don't say!
 
Without knowing an overall design it's impossible to be sure, but from what you've described I would keep the TNS throughout (double check your earth conductor requirements using the adiabatic, but I'd have thought a 16mm SWA would be sufficient csa eq.) and just look at fitting RCD protection at 300 or 500mA only to locations where they may be risk of fire (think about dust etc). If the design has been done properly and discrimination taken into account then there shouldn't be any tripping issues anyway.

However........I suspect that it's probably like any other farm I've ever been on and is a real spider-web mess of DIY electrics and broken kit!!
 
Why would you make a grain house TT?? I can understand where livestock is involved.

here...some livestock:

[ElectriciansForums.net] agricultural tt earth

keep the mice down....

you`l need to construct a faraday cage for it...
 
You do not have to go TT as no livestock will ever be about ( As long as you are absolutely positive of this ! ) , but you will need to protect everything with a RCD of no greater than 300mA ( Used to be 500mA for he 17th , but has now changed to this for the 16th ) , you could even drop this to 100mA , but as most grain handling systems are now starting to go inverter drive you may have issues with just 100mA of fault protection , and don't forget it wants to be an s-type .
As for placing it at source , in the house , or at the first shed , only you know the site conditions .
 
Last edited:
The main swa from house is 16mm 4 core, swa as earth.

Nope, using the SWA for your main earth to this grain shed is a non starter, the Armouring will not comply where main bonding is also required, it's only suitable for purposes of providing the cables CPC.... You're going to need to provide a separate earth conductor, 10mm minimum.
 

Reply to agricultural tt earth in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
660
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top