M

mungo9

I have recently completed my first job and it was an extension to my Uncles house. i haven't qualified yet but the job went well and everything works, although i have 1 issue. Due to my lack of experience where my uncle was trying to save money on the job he said he didn't want smoke detectors wired in and would buy them separately, obviously i normally wouldn't say thats okay. However now the job has ended and the Building inspector is coming round soon, i realise to be safe and make sure everything passed i should have just put them in. I still need to choose the battery powered smoke and heat detectors that will pass.
Can anyone tell me what battery powered smoke dectectors i should get? and if they comply with the regs.
 
Personally I think this has been the most worrying and confusing thread I read up to date.
And a read of the BS5839 sounds well over due as professional sparks.
Posts have mixed up Part6, Part 1 , Grade A, Grade D, and Grade F which all have their own standards, and places. So lets look at it.


1. Supply isolation is grade A (Fire control panel)
2. Grade D does not require a separate dedicated supply (due to battery backup)
3. Grade E does require a dedicated supply circuit (due to no battery backup) Grade F battery only detection, can only be used in private dwellings, being customers choice. A variation agreement maybe reach to fit Grade F (such as listed building)
4. Building control are there for a reason, and actually hand it to you on a plate...or drawings in this case.
Dont follow their instructions...and you will get burnt.[/QUOTE]


I'm not sure where the confusing parts are but yes lets look at it.


OP starts by saying he has forgotten wiring for smokes on a rewire and building control is involved in some fashion.
Members then say he can have wireless smokes wired off the lighting.


So we have no cables for a "Grade E system" and when using lighting circuit for mains that's a "Grade D system".
So as already stated a "Grade D system" has an independent circuit (dedicated) OR regularly used lighting circuit (not any old circuit is it).
A member then posts a link to some battery only radio smokes as a "get out of jail", so I click on link and
then read the data sheet regarding the said smokes (yes I'm sad) where it states they will only satisfy to a "Grade F" system.
It appears some people failed to click on link and then read the spec. But ha ho


I don't have my copies of BS 5839-1 & 6 on this computer (they're on work computer) but I do have a copy of
"Electrician's Guide To Fire Detection And Alarm Systems" on my shelf (for quick ref) where right or wrong as I said "I believe" where it says
for dwellings power supplies approved document systems we have "single independent circuit" blah blah "regularly used lighting" blah blah "jump through hoops about RCD's" blah blah
we then get to the line saying "The Approved Document requires a means of isolation for
the fire system supply so that it can be isolated with the lights on. This will need to be labelled so that its purpose is clear."


Now with out checking BS 5839-6 until tomorrow (if I can be assed) that statement whether true or not is basically saying it needs isolation for testing and maintenance.
I know Approved Documents have been updated/changed the same as other documents.
But I would imagine this guide (yes guide) is probably correct and can see no reason for its removal (could be wrong).


Not sure where BS 5839 -1 comes into thread.
Not sure where "Grade A" system comes into thread.


If your still confused get yourself a beer/glass of wine and turn computer off, life's to short.
 
A Grade A system part 6 requests your revert to Part 1. As this will now be your standard to install a full fire alarm system.
Local isolation is only required on a control panel...Grade A/part 1.
Now time for my beer, As I have given the specs..where to look, and what is required.
 
Well in dwellings you should be working to "Approved Document B Volume 1"
Where on page 14 it states under power supplies "There should be a means of isolating power to the smoke alarms without isolating the lighting"

Now where is my lighter for my cigar lol
 
Thank you for the lastest copy mine was out of date.....As Document B be suggests smoke detection should be taken from dwellings db direct or grade D from lighting circuit. Smoke detection POWER SUPPLIES should be taken from the main db with isolation. ie the fire alarm control panel, as mains smoke detection is not supplied from a POWER SUPPLY.....I admit, it is misleading, but is aimed at a control panel not a mains smoke detector.
 
I have seen this phrase used alot recently "smoke power supplies" basically the control panel which supplies the smoke detection. I think it very misleading, but if you read the section you mentioned on page 14, you can see it applies to Grade A/part 1 of using double pole isolation.
 
And a control panel with its own power supply...........you dont connect mains powered smoke detectors to a power supply..?

No because they have an integrated one.. and are called smoke alarms.
They are a self contained power supply, backup supply, detection and sounder all in one.
 
[ElectriciansForums.net] Smoke detector help please

I give up.. read it how you will lol
 

Reply to Smoke detector help please in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
708
Replies
1
Views
301

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top