M

mungo9

I have recently completed my first job and it was an extension to my Uncles house. i haven't qualified yet but the job went well and everything works, although i have 1 issue. Due to my lack of experience where my uncle was trying to save money on the job he said he didn't want smoke detectors wired in and would buy them separately, obviously i normally wouldn't say thats okay. However now the job has ended and the Building inspector is coming round soon, i realise to be safe and make sure everything passed i should have just put them in. I still need to choose the battery powered smoke and heat detectors that will pass.
Can anyone tell me what battery powered smoke dectectors i should get? and if they comply with the regs.
 
But its a building reg! not a recommendation like the BS books.

Take your mains smoke alarm from the lighting circuit.
Read the instructions for the smoke alarm (Aico will do) and it clearly states "Disconnect main before removal" referring to the unit.
The building reg states.....There should be a means of isolating power to the smoke alarms without isolating the lighting.
So how do you isolate the supply to the smoke alarms without turning the lights off?

Its not rocket science is it...
First he says there not smoke alarms now he says they are but forget the building regs...
 
Have asked a few bsi trainers, Aico and kiddie for their views, All manufactures smoke alarms meets required EN standard to allow their detectors to be installed to BS and Document B without the need for separate isolation....this is achieved by using a anti tamper base, which can only be removed by using a tool, such as a screwdriver. Bases have been manufactured to allow safe disconnect, without exposing live conductors. And thus comply.
 
Last edited by a moderator:
Please show the whole of the section instead.of trying to mislead members... as you can see from notes 1 and 2 the mcb suppyling the circuit, and the base of the detector itself forms the isolation for maintenance...!!! Have contacted Aico to confirm, no isolation is required, as wired base conforms to methods required for maintenance, and isolation.

15 Power supplies
15.5 Recommendations for power supplies for Grade D
Systems
a) ii) a separately electrically protected, regularly used local
lighting circuit in which case there should be a means for
isolation of the smoke alarm(s) from the lighting circuit (e.g. for
maintenance).
NOTE 1 This does not imply that there need be separate
Electrical protection of the smoke alarm circuit; a single means
of protection against overload or short circuit (e.g. a fuse or
miniature circuit breaker) serving the entire circuit is
acceptable.
NOTE 2 A number of manufacturers use a fixed base for the
electrical connections, and the smoke or heat alarm can be
readily removed by use of a tool operated release tab, etc.

I'm sure I read that they couldn't be on an RCCB that protected a socket circuit?
 
I was taught that one circuit shouldn't affect another circuit

It wouldn't if the smoke alarms are on the lighting circuit. No circuit other than the lighting circuit would be affected.

And as said there's no reason particularly why it need affect the lights on the lighting circuit (depending on the exact nature of the work being carried out).
 
Whats has a socket circuit, got to do with this thread...??

I thought I had read that they had to be on a dedicated circuit and one that in the event of tripping didnt knock out sockets.

That's what I meant by I thought they couldn't be on an RCCB that covered sockets.

BS5839-6 states that :-
i) The r.c.d. should serve only the circuit supplying the smoke alarm(s) and heat alarms OR
ii) The r.c.d. protection of a smoke alarm circuit should operate independently of any r.c.d. protection for circuits supplying socket outlets or portable equipment.

Or am I reading this all completely wrong
 
I thought I had read that they had to be on a dedicated circuit and one that in the event of tripping didnt knock out sockets.

That's what I meant by I thought they couldn't be on an RCCB that covered sockets.

BS5839-6 states that :-
i) The r.c.d. should serve only the circuit supplying the smoke alarm(s) and heat alarms OR
ii) The r.c.d. protection of a smoke alarm circuit should operate independently of any r.c.d. protection for circuits supplying socket outlets or portable equipment.

Or am I reading this all completely wrong
a lighting circuit isnt a portable appliance you halfwit
 

Reply to Smoke detector help please in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Personally I won't do fixed price work unless there is a clear spec for the job including things like smokes, data, TV whatever else the customer...
Replies
3
Views
708
Replies
1
Views
301

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top