Search results | Page 9

Search results

  1. T

    220V 3 Phase?

    Check this thread out, i had never seen one before untill i read this Tim 240v 3 phase plug? http://www.electriciansforums.net/showthread.php?t=72192
  2. T

    IR method 2

    Hi guys, What plug in equipment, if any would show a dead short when doing an ir test? I have the line and neutral connected together and testing between that and the earth bar. The circuit was energised and working fine on arrival (doing an eicr) so it cant be an actual dead short or the mcb...
  3. T

    Eicr code - db is dirty

    A pic of the entire db so you can all get the full picture. The cables at the top have been crushed by the board cover, no major damage yet, but its only a matter of time. The top and bottom entry holes have no form of gromit, the main switch is upside down, getting to the neutral and earth...
  4. ImageUploadedByTapatalk1363105110.984177.jpg

    ImageUploadedByTapatalk1363105110.984177.jpg

  5. T

    Eicr code - db is dirty

    You are right, ive noted it as a c3 as the db was suitable for the environment untill is was damaged allowing grime to get in, though i think i may change it to a c2 otherwise they wont bother fixing it
  6. T

    Eicr code - db is dirty

    I did check, and it was definatly live, i have now disconnected it from the dp isolator. Volt sticks are good for indication, but i wouldnt bet my life on them Cheers, Tim
  7. T

    Eicr code - db is dirty

    Ill agree with the concensus that im being pedantic, ill include it in the code for the broken door hinge. Cheers guys, Tim On a side note, look what i found above the sink. Code 1 i think. (I will fix this on site obviously) And no dissing the voltage detector, they have their uses...
  8. ImageUploadedByTapatalk1363083709.185332.jpg

    ImageUploadedByTapatalk1363083709.185332.jpg

  9. T

    Eicr code - db is dirty

    Hi guys, Im doing an eicr on an events building, the db is in the main kitchen, however dirt and grime havegot into the db. Would you code it? Im thinking c3 as there is no sign of danger but improvements could be made. Or am i being too picky. The cause of the grime getting in is the fact...
  10. ImageUploadedByTapatalk1363082063.471178.jpg

    ImageUploadedByTapatalk1363082063.471178.jpg

  11. T

    LED TUBES REPLACING NORMAL 6ft T8 HF .....HEADACHE not working

    As above, and also remember that most led tubes only need 230v to one end of the tube
  12. T

    Wiring of 3 Phase 63A Distribution Board

    Malaysia, that explains it, i was thinking that was a bit overkill for a 2 bed semi.
  13. T

    Submain with no isolation

    I could not find a reg that said if the submain run is less than 3m it does not need OCP. So that is definatly going in the report with a recommendation to upgrade the db isolator to an OCPD as you said. A picture through the gap, unless im very mush mistaken, these are not 315a bs88's...
  14. ImageUploadedByTapatalk1362128494.464126.jpg

    ImageUploadedByTapatalk1362128494.464126.jpg

  15. T

    Submain with no isolation

    Untill i can open the isolator i cant confirm 100% if or what OCPD is protecting the busbar. Im hoping i can get in at the weekend to check, from what little i can see though there are just 1" by 1/4" links, so only an isolator. The previous periodic says that there are 315a bs88 fuses in the...
  16. T

    Submain with no isolation

    I hope you can see the picture. 2 of the 3 armoured cables on the right feed the DBs mentioned the 3rd feeds an isolator for a seperate db in the cupboard. The main isolator at the bottom is only an isolator, no fuses as far as i can see, i cant fully open it though. Tim
  17. ImageUploadedByTapatalk1362055513.932739.jpg

    ImageUploadedByTapatalk1362055513.932739.jpg

  18. T

    Submain with no isolation

    I cant fully open the isolator without turning off the entire building, from what i can see by undoing the screws and peering in to the 315a main isolator they are only links, no fuses. Ill go take a pic of the intake layout.
  19. T

    Submain with no isolation

    Hi guys, Im doing an eicr on a commercial site (offices) and have found 2 3phase db's fed strait from the main intake busbar. 1 run is only 2metres clipped direct armoured 35mm 4c And 1 is 8m clipped direct above ceiling tiles armoured 25mm 4c Am i right in saying they need a fused isolator...
  20. T

    where can i get a copy of GS38?

    My megger 1730 came with little tips to reduce the exposed bit to 1mm or so. I assume the 1552 did too, maybe they have been lost Tim