Just note it in the comments section and that you have carried out as far as reasonably practicable testing to verify that the water pipe has a relatively low resistance to earth. What else can you do?
Please with the fire rating malarkey, it’s irrelevant, it’s no different to installing a mains tails gland, the IP rating of the CU needs to be maintained, that’s it.
Taken from Hager’s CU instructions
TNC-S, TN-S when installed in an electrical installation complying with BS 7671
Hager recommends for TT systems a 100A type S time delayed RCCB or a main switch with RCBO protection only on all outgoing circuits.
If supplementary bonding is required then each circuit serving the location is required to have a connection between the cpc terminals of any class 1 and class 2 accessories/equipment and to any accessible extraneous pipework, water etc.
Wilko’s picture explains.
On the cast iron cut out query, Clients in my experience have basically said that they can’t afford the down time in having one changed where the premises is 24hr occupied so they never get it replaced, now whether or not the DNO have insisted it’s changed as it’s their equipment , I don’t know.
If supplementary bonding in a bathroom is applicable then Bathroom supplementary bonding needs to connect together the terminals of the protective conductor of each circuit supplying class 1 and class 2 equipment and to the accessible extraneous conductive parts (water pipes etc) or if there’s...