Is spurring off a sockets that’s already been spurred off a major no no?? It’s for a socket behind a wall mounted tv so not gony be a major load on the cable
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Spurring of a spurred socket in the UK Electrical Forum area at ElectriciansForums.net
It is unless you connect a FCU into the equation as per the Appendix 15Is spurring off a sockets that’s already been spurred off a major no no?? It’s for a socket behind a wall mounted tv so not gony be a major load on the cable
Speak for yourself - I live royally off the commission from reporting such naughtiness....as above^^. it's not compliant, but you won't get dragged away by the IET Gestapo and have your sidecutters surgically removed.
Don't you mean his testiquipment?as above^^. it's not compliant, but you won't get dragged away by the IET Gestapo and have your sidecutters surgically removed.
While not technically compliant I can see no real problem with spurring a single socket from another single socket which itself is a spur. .
Technically not rightWhile not technically compliant I can see no real problem with spurring a single socket from another single socket which itself is a spur. The reasoning being that the number of outlets on a spur is the same as a compliant twin socket fed as a spur from a ring. Any other scenario of more than one outlet from a spur would require being supplied through a 13a fused connection unit to avoid the possibility of overloading the spur conductors.
It is far better though to avoid spurs and feed all outlets by properly extending the ring.
No his electrical qualificationsDon't you mean his testiquipment?
Well you should be.Don't you mean his testiquipment?
Don't make it compliant though does itThere is an argument for this, though that would assume that the cable is not derated at all during its run as 26A is in best circumstances. And I doubt anyone is going to do the calculations or written risk assessment to cover themselves in a court if something were to happen...
Most double sockets are rated at 20A I believe, not 26A, partly for this reason - And many of the cheap sockets would probably struggle with 20A from the state I've seen some of them when installed in kitchens.
I recently found a 2.5mm radial covering kitchen and downstairs which had been on a 32A MCB for at least 10 years. The cable passed IR testing perfectly - though some of the sockets had to be replaced for melty connections.
Don't make it compliant though does is it?There is an argument for this, though that would assume that the cable is not derated at all during its run as 26A is in best circumstances. And I doubt anyone is going to do the calculations or written risk assessment to cover themselves in a court if something were to happen...
Most double sockets are rated at 20A I believe, not 26A, partly for this reason - And many of the cheap sockets would probably struggle with 20A from the state I've seen some of them when installed in kitchens.
I recently found a 2.5mm radial covering kitchen and downstairs which had been on a 32A MCB for at least 10 years. The cable passed IR testing perfectly - though some of the sockets had to be replaced for melty connections.
Technically not right
But your not going to put any cables or terminals under any sort of stress doing this. Still going to pull 26A Max.
The point about double sockets being rated at 20a has been levelled against this before, but in practice no punter will take this into account when plugging appliances in. If they want to plug in 2x 3kw heaters they will plug them into whatever is there, be that a twin or two singles. The same applies to the rating of the cable, whether it is a twin spur or two singles it can still be subject to exactly the same load.There is an argument for this, though that would assume that the cable is not derated at all during its run as 26A is in best circumstances. And I doubt anyone is going to do the calculations or written risk assessment to cover themselves in a court if something were to happen...
Most double sockets are rated at 20A I believe, not 26A, partly for this reason - And many of the cheap sockets would probably struggle with 20A from the state I've seen some of them when installed in kitchens.
I recently found a 2.5mm radial covering kitchen and downstairs which had been on a 32A MCB for at least 10 years. The cable passed IR testing perfectly - though some of the sockets had to be replaced for melty connections.
Yeah, I’m only saying in theory like we all are, would never install i that way ?Probably true - though I'm sure someone could find an unfused euro pin adapter and take rather more - not that unusual I'd suspect in a rental property.
That's why compliance is always the best option - then it's never your fault when the end user does something stupid....
The wiring regulations are not statutory, and departures are permitted where it can be demonstrated that the resulting degree of safety is not less than that obtained by compliance.The wiring regulations are there for a reason. A spur off a spur is non compliant. Simple as.
If this first spur was taken from a 16A radial circuit, then that's a different story.
(cough change the breaker cough)
Yes. I know... Very simplistic solution. I dont know how many points are on the circuit already.... might be all of downstairs with kettles and heaters and whatever else.
If its an easy enough job, FCU at the source of the spur, as suggested above. Then everything taken off is limited to 13A.