Search results | Page 3

Search results

  1. dokkan1080

    Flats with 10mm twin and earth

    If method A 61 amps?
  2. dokkan1080

    Flats with 10mm twin and earth

    The gas and water are both 6mm but some one has also run 10mm to them no idea when that was. Main earth is 6mm from the 16mm twin. If I wanted the board changed would I need to have a 16mm earth run? A new earth could be run easy straight out the wall and down to where the main intake is...
  3. dokkan1080

    Flats with 10mm twin and earth

    Its the same in my flat 16 mm twin 6mm earth The bonding conductors are bigger than the 6mm earth
  4. dokkan1080

    Flats with 10mm twin and earth

    Seen loads of flats are fed from a 60amp isolator in 10mm twin and earth? don't they need to be 16mm tails and at least a 10mm earth? or is it just down to the adiabatic?
  5. dokkan1080

    Brought a new oven

    The oven 2.9kw which is 13amps so its 3 amps under the 16 amp breaker does it comply and as its not arrived yet I cant see the specs for installation
  6. dokkan1080

    Brought a new oven

    Thats what I thought thanks so 13amps on 16amp mcb is fine then?
  7. dokkan1080

    Brought a new oven

    The oven i brought for my new flat is Bosch HBS534BS0B I have a cooker circuit thats on 40 amps fed in a think its 6mm not sure it might be 10mm is there any easy way to tell 6 and 10mm apart? If the cirxuit is downgraded to 16 amps can that oven be wired into the cooker outlet point
  8. dokkan1080

    Mk 7860 uplift

    How can I get a 3 wire no trip test of between 2ohms and 1114 ohms But on a high current test get 0.19 between live and earth and 0.1 between live and neutral. When the rcd is bridged out I can do the 3 wire test and get a sensible zs of 0.2 ohms. The strangest part is the first 2 sockets on...
  9. dokkan1080

    Continuity between live conductors

    Thanks for the replies :) I was just curious as all....before I brought the property the neutral in the main switch had burnt out. And the board was replaced, what would cause that? Would the neutral cable have just become loose over the past 40 or 50 years or could the problem have been...
  10. dokkan1080

    Continuity between live conductors

    Ah that makes sense. ? I will try that in the morning. so with Insulation Resistance Though you can test off the neutral bar and or earth bar and the breakers though right?
  11. dokkan1080

    Continuity between live conductors

    On my cu at home I have a continuity reading between my ring final circuit and a radial circuit of 114ohms between live conductors. When I test continuity from each breaker. Why would that be? Break down of cable If I turn one off and leave the other on I don't get a voltage. At what point...
  12. dokkan1080

    Main earth run outside?

    If its in black plastic conduit?
  13. dokkan1080

    Main earth run outside?

    Can the main earth be run on the outside of a building from the MET to the consumer unit clipped direct? Would it not need some form of protection
  14. dokkan1080

    Live earth neutral and the cut out fuse

    So earth and neutral are the same they just go into different bars in this case... The neutral is the return path so why does the circuit breaker operate when the earth is turned into the return path in the case of a fault....if they are the same
  15. dokkan1080

    Live earth neutral and the cut out fuse

    And that gives continuity across everything :/? Its hard to visualise it?
  16. dokkan1080

    Live earth neutral and the cut out fuse

    Learning and curious At my home the neutral and earth are joined by the cut out fuse. The neutral goes up to the meter and the earth goes straight to the board. I can't wrap my head around how the earth and neutral are different? When the cut out fuse is out ( some one broke the seal along...
  17. dokkan1080

    Ip44 230v zone 1?!

    You said you would use a higher ip rated fitting but the ip44 fitting complies? Its hard to find ipx5 or 6 or 7 lights i have been looking for ages :/
  18. dokkan1080

    Ip44 230v zone 1?!

    This is how it is ip44 or do I get a higher fitting
  19. dokkan1080

    Ip44 230v zone 1?!

    I want to put it above my shower its a small shower room so the tray takes up most of the room... From the tray to the ceiling it measures about 2.15m so the light would be just above the shower head But from the floor to the ceiling it measures 2.4m there is a massive step into the shower

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top